UK Cable Maximum Allowable Current - Electrician Talk - Professional Electrical Contractors Forum
Old 05-12-2015, 03:13 AM   #1
Rewards Points: 52
Default Cable Maximum Allowable Current
My factory will install 75kW 3 Phase Motor (415V) and by using 3C x 35mm2 Armoured Cable.
Based on IEC standard, is that the cable enough to withstand the maximum current produce from 75kW motor?
Please attached the IEC data if available.
Thanks.
atjm88 is offline   Reply With Quote
Old 05-13-2015, 12:14 PM   #2
Very Long Vacation
Rewards Points: 5,262
This I would use:
http://www.batt.co.uk/upload/files/4d5.pdf
Old 05-17-2015, 06:20 AM   #3
rollin' with doube d's
Rewards Points: 109
Without knowing intended installation method / environment / cable distance / motor wiring configuration I couldn't answer this (at least to Australian standard.)
75 kW is 130A, 35mm2 PVC insulated cable won't handle the temperature rise and will melt at this current draw, I'd be bumping it up to 50 mm.
maddhatter is offline   Reply With Quote
Old 05-22-2015, 03:06 AM   #4
Rewards Points: 52
Originally Posted by meadow View Post
Thanks. How to get higher mm2 data?
Old 05-22-2015, 03:07 AM   #5
Rewards Points: 52
It'll be on cable tray open air, the distance is 150m. The motor wiring you mean is Star / Delta is it? If yes, how much different for both? Thanks.
Old 05-22-2015, 04:52 AM   #6
Rewards Points: 109
To satisfy a voltage drop of 2.5% @ 130 Amps for PVC sheathed SWA you'd need to run 95mm2 cable.
If the motor was in 6 wire delta configuration, you could downsize the conductor size but you'd be better off just sticking with 95mm2.
I'd get my calcs independently verified before taking the word of some random on the internets.
Cable Maximum Allowable Current atjm88 General Electrical Discussion 18 04-20-2015 07:03 PM
Cable Maximum Allowable Current atjm88 General Electrical Discussion 11 03-05-2015 05:43 AM
14 AWG allowable ampacity shocking NEC Code Forum 31 05-09-2013 04:11 PM
For Sale: Current Mantis 8890 Cable Puller K&R Electrician Swap 0 05-14-2012 09:21 AM
Condux and current cable pullers K&R General Electrical Discussion 4 06-08-2007 07:46 AM