Originally Posted by Jerry Revels
What are the issues with wiring a UERO or UK style rreceptacle that requires 1 line / or ungrounded conductor, 1 neutral and a grounding or Earthing conductor with typical US 208 or 230 volt supply with 2 line / or ungrounded conductors and a grounding conductor. The obvious is there is no netural and the device is not being wired as intended and it is not providing polarity. It works because I have seen it in use but the question is:
[/list]
It works fine
- is it a sefety risk and if so why
Depends on who and how the circuits were installed.
- are there any refferences showing this as a code violation in the NEC.
No, not that I am aware of.
- Also direct wiring of equipmet such as forced air heaters listed for 230v to ground Euro sytle power.
Only problem is if the circuit the equipment is plugged into/ connected to is GFCI protected. Some European equipment have a higher ground current that will trip a GFCI. A GFCI will trip at about 4-6 mA whereas a RCD will trip at about 30 mA. This is where you might get into some NEC code issues.
And BTW welcome to the forum.