UK Motor overload settings - hazardous area - Electrician Talk - Professional Electrical Contractors Forum
Like Tree2Likes
  • 1 Post By JRaef
  • 1 Post By gnuuser
Old 04-13-2016, 04:53 PM   #1
Rewards Points: 8
Angry Motor overload settings - hazardous area
I have an Exd motor located in a zone 2 hazardous area. The FLA is 18Amps, the Locked Rotor Current is 24Amps. The motor drives a mud tank agitator with a variable load, depending on the weight of fluid in the tank. My question is, What should the overloads be set at?
I can give some more details of the type of overloads installed if required.
John Thomson is offline   Reply With Quote
Old 04-13-2016, 09:18 PM   #2
Rewards Points: 2,558
Most IEC overload relays will be factory calibrated so that you set them for the actual motor FLA as it shows on the nameplate. The pick-up point of 115-117% is already factored into the design based on you having done that.
John Thomson likes this.
Old 04-14-2016, 05:37 AM   #3
Rewards Points: 8
Thanks very much for that, do you know of any trade/manufactures documents that would confirm this? Also any trade/manufactures documents on 'motor start mounded case circuit breakers would be appreciated. Thanks in advance J, your quick response is appreciated.
Old 04-14-2016, 07:25 AM   #4
Rewards Points: 2,755
That would be in installation information from the manufacturer of the overload. Do you have that information? Or at least a manufacturer and part number?
AK_sparky is offline   Reply With Quote
Old 04-17-2016, 09:47 AM   #5
gnuuser's Avatar
Rewards Points: 1,654
quite often they are usually set for the motor rating but it should also be taken into consideration the size of the conductors.
more than a few times iv'e found the setting was raised due to nuisance tripping (usually by an unauthorized person)
even worse when the conductors were undersized for the distance from the supply and a larger motor had been later installed without changing to the proper size conductors.
its one of these deals where you have to look at everything with a careful eye
Old 04-24-2016, 08:18 PM   #6
Rewards Points: 8
Thanks for that, food for thought.