Old 12-15-2011, 05:03 AM   #21
Frank Mc's Avatar
Originally Posted by micromind View Post
One reason is because old-timers can repair a wye-delta starter, but not anything electronic.
Who do you define as oldtimers????......
Only our rivers run free
Frank Mc is offline   Reply With Quote
Old 12-15-2011, 05:17 AM   #22
Originally Posted by dronai View Post
I found this on another site. I figured someone here would know. Looks to be IEC standard, not Nema
We have a 125 HP, 3 phase, 480VAC motor that has six leads coming out of the motor. Two leads are labeled "U2", two are labeled "V2", and two are labeled "W2". So I have 3 pairs of leads with the same label on them. Checking resistance between any two of the leads labeled the same indicates no continuity. However, you can read continuity between a U,V,W set. This indicates to me that there are two independent sets of motor windings. The debate between my co-workers is how to connect this motor. The thoughts are to connect both wires labeled the same to a leg of 3 phase. The other is to only connect one set of windings to the 3 phase. By the way, the motor cover shows a connection diagram for 9 wires. Any help is greatly appreciated.
That is double "delta" connection that is little odd for straight 480 volt hook up.( for the IEC type motours unless they are large motor size then it will be common )
There are some case you will see same size tails that can be part winding start.
Whatever the reason if you have VFD or start on DOL { direct on line } on smaller motours always wired them up in delta otherwise you will burn up the windings { not very often you will see double Wye connected for running mode.}
The otherwise the Motourwinder did have the correct sequince of connections ditto with dronai's link for the connection.
Merci,
Marc
Old 12-15-2011, 06:13 AM   #23
Originally Posted by HARRY304E
Who is a stiff..?
Only the self proclaimed one
Gaterhater is offline   Reply With Quote
Old 12-15-2011, 10:10 AM   #24
Motorwinder's Avatar
Merci,
Marc
Not a delta. If you have continuity U, V and W, that indicates internal wyes. If it was delta or wye/delta, You'd have continuity between 3 pairs. Probably wouldn't be able to run part-winding either. It's possible, but why would a winder connect a part-winding connection and not mark it accordingly. Someone rewound it and brought out 6 leads is all.
Motorwinder is offline   Reply With Quote
The Following User Says Thank You to Motorwinder For This Useful Post:
frenchelectrican (12-16-2011)
Old 12-15-2011, 10:39 AM   #25
Fond of three phase
Originally Posted by Motorwinder View Post
I really am a motor winder BTW. This is the one I did today..
Back to the regular scheduled program..
Looks like the kind of motors we used to build. Worked at the Louis Allis Co. in Milwaukee 33 years. I see you have VPI equipment. Do you also do form-coil jobs as well. Very interesing business. It keeps you on your toes.
retiredsparktech is offline   Reply With Quote
Old 12-15-2011, 11:09 AM   #26
Louis Allis were good motors.
We do motors up to about 5000hp depending on weight.
This was an 1100 HP. We've done several of these for a local water district.
The Following 4 Users Say Thank You to Motorwinder For This Useful Post:
76nemo (12-15-2011), dronai (12-16-2011), micromind (12-15-2011), retiredsparktech (12-15-2011)
Old 12-15-2011, 11:22 AM   #27
Fond of three phase
I see you have the most important piece of equipment pictured. The coffee pot. Great job on the form coil.
The Following User Says Thank You to retiredsparktech For This Useful Post:
Motorwinder (12-15-2011)
Old 12-15-2011, 08:17 PM   #28
Here is the NEMA and IEC wiring drawings from the EASA handbook.
http://www.goevans.com/EHB_pgs0803.pdf
The Following User Says Thank You to John Valdes For This Useful Post:
dronai (12-15-2011)
Old 12-15-2011, 08:51 PM   #29
How many speeds/FLA's on the nameplate?
SteveO. is offline   Reply With Quote
Old 12-16-2011, 04:09 AM   #30
That what I am thinking as well if someone did rewound it and did not mark it properly it can leave a nasty suprise if not heeded.
Merci,
Marc
new lead man rnr electric Residential Electrical Forum 178 07-17-2011 11:41 PM
Lead anchors for j-box Saloomen NEC Code Forum 45 07-01-2011 08:39 PM
Lead services Gamit Business, Marketing, and Sales 8 06-28-2011 08:05 PM
need help with a 12 lead motor ArcRedoubt PLCs, VFDs, Motors and Controls 10 06-15-2011 10:29 AM
Lead Paint Speedy Petey General Electrical Discussion 21 04-20-2010 11:30 PM