Old 05-03-2012, 10:02 PM   #1
Electron Flow Consultant
sparky970's Avatar
Default control power transformer
What would you expect to see for resistance from h1 to h2 on a 480v to 120v cpt. I have one that I measured at 54 ohms. Seems a little high.
Old 05-03-2012, 10:04 PM   #2
Zog
Zog's Avatar
Depends on the CPT ratings.
Old 05-03-2012, 10:14 PM   #3
sparky970's Avatar
I don't have it with me, but it's an old Cuter Hammer C340CG. I think that's the number. It's a .105kva.
Old 05-04-2012, 08:55 AM   #4
Zog
Zog's Avatar
Sounds reasonable, depending on what you used to take the reading.
Old 05-04-2012, 12:13 PM   #5
Ohms law? You have a nameplate? Right?
Old 05-04-2012, 02:12 PM   #6
Just out of curiosity, why do you care?
Old 05-04-2012, 03:48 PM   #7
Zog
Zog's Avatar
I was going to ask that too.
Old 05-04-2012, 04:30 PM   #8
Tom45acp's Avatar
Ohms Law? You don't need no stinking ohms law,especially since it does not take into account inductive reactance.
Sometimes I wonder whether the world is being run by smart people who are putting us on, or by imbeciles who really mean it.
Tom45acp is online now   Reply With Quote
The Following User Says Thank You to Tom45acp For This Useful Post:
Zog (05-04-2012)
Old 05-04-2012, 04:32 PM   #9
But you didn't...
Old 05-04-2012, 04:47 PM   #10
sparky970's Avatar
I had a trouble call. 480v motor, about 160v to ground on A phase. Pulled bucket, checked bus voltage. Meggered breaker, starter, and motor. Everything was fine. I had disconnected the load side of the breaker and I put the bucket back in and all the voltages were fine. Didn't see any bad connections either. I took the starter apart today and found a tiny piece of plastic but couldn't see where it came from. Contacts weren't pitted, but there were a few spots on the plastic near the contacts where it looked like it may have gotten hot
Old 05-04-2012, 05:14 PM   #11
Splash's Avatar
You don't need to worry about inductive resistance. Ohms law applies to the primary and secondary side independently. All you really care though is whether one side is not shorted or open.
Splash is offline   Reply With Quote
Old 05-04-2012, 05:58 PM   #12
I don't know what that would have to do with the resistance of the CPT. Sounds to me like a motor or motor lead problem. Did you megger the motor and leads?
If you are not responsible for the motors (in some facilities that's a Millwright's job), then you did what you needed to do, you elimiated the other possibilities. I wouldn't waste any more time on the CPT. If you get the right voltage out of it, it's fine.
Old 05-04-2012, 06:49 PM   #13
sparky970's Avatar
I did megger the motor and leads. I had just done a simple resistance check on the cpt. Couldn't find any issues with anything else.
Gas Log Control/Fan power Junction nchvac General Electrical Discussion 0 02-09-2012 01:35 AM
Control transformer Drdwlee General Electrical Discussion 20 07-10-2011 01:22 AM
control transformer. captkirk General Electrical Discussion 48 06-08-2011 11:31 PM
Control transformer opinion jaymh Services and Service Equipment 5 08-18-2009 05:04 PM
Speed control and power consumption Keln General Electrical Discussion 2 02-10-2009 11:17 PM