Old 10-31-2010, 05:15 PM   #1
Default Help with a Delta Electronics VFD-B
Manual at: http://www.delta.com.tw/product/em/d..._manual_en.pdf
I have a Delta Electornic VFD-B drive. I have the 3-wire Stop/Start and FWD/REV figuered out using NO for run,NC for stop and 3 position sl sw for FWD/REV just like the drawing on page 5-19. My issue is this drive will be installed on an inclined convyer with a external brake so when it stops it doesnt rollback. There will be people working right on the line so needless to say they will be starting and stopping it. Now I want to use one of the multi-function inputs for a one step speed control, but I feel if I install a on-off selector sw for this someone will forget it is engaged and start it with it on. What is the best way to wire a NO momentary sw and still maintain the input when pressed? If I use a 24V relay in the input circuit do I need a diode across the coil? Also I have never worked with an external DC motor Brake but it looks pretty straight forward. I'm just using existing brake already installed in the field any advice?
sparkytwig is offline   Reply With Quote
Old 10-31-2010, 11:47 PM   #2
I void warranties
Jlarson's Avatar
Gawd the user's manual is like 5 MB's, WTF?
The best never stop learning.
Old 11-01-2010, 05:49 AM   #3
If this drive has a NO contact output (most do) then run whatever control power that you have through this contact to a relay rated to handle the brake coil load. Program the contact output to close on "drive running". Almost all motor mounted brakes are energize to release.
I am assuming that you know that the brake CAN NOT be powered from the drive output to the motor.
Old 11-01-2010, 11:22 AM   #4
If you are using a brake motor and VFD, you must separate the VFD output from the brake. The brake needs it own power supply and can be energized and de-energized from a drive output.
I am not certain what you mean by this? Of course you can use a preset speed via contact closure. The drive can be programmed to start with another input (start). The preset speed can be jumped in the drive panel if you want, so no one can mess with it.
Just give them access to stop/start and you keep control of the speed.
The drive is programmed to either 2 or 3 wire control. In 2 wire control, when the input is closed it's not maintained. Its like jog. In 3 wire control, when the input is closed, it stays closed without any further requirement. That's the difference between 2 wire and 3 wire control.
Physically jumper the preset speed you require. Then all you need is a stop/start switch for the operators.
The Following User Says Thank You to John Valdes For This Useful Post:
sparkytwig (11-01-2010)
Old 11-04-2010, 09:48 PM   #5
Most brakes are wired as a fail safe, wire your contractor control to RC and RA, N.O., then set 03-00 to 1 ac drive operational, when drive is operating the contractor will energize releasing the brake, set the drive to coast to stop or you will get a dc bus over voltage when you stop
Hunter1151 is offline   Reply With Quote
Old 11-05-2010, 11:42 AM   #6
Now, lets try that again in English. RC? RA? 03-00? 1 ac drive? contractor?
Old 11-05-2010, 12:50 PM   #7
this drive has a single pole double throw form C Relay, We will control the holding break with a contactor, assume 120V coil, we can wire to the terminals on the drive RC, this is the common side of the form C Relay, then to RA, this is the switched side of the Form C Relay.
Now we will program the drive to close that relay when the drive is operational. Under Group 3 Output Function Parameters (03) we can then goto Multi Function Output Relay Setting (00) so the parameter you need is 03-00, Set this to 01 - AC Drive Operational. So when the drive gets a command to start, the relay will change stated energizing the coil applying power to the dreak and releasing it, if the drive faults or is shut off the relay will open denergizing the contactor coil, removing power from the break and now it is holding.
Old 11-05-2010, 12:57 PM   #8
I have a better idea.
Turn brake on when drive is in stop mode. Turn brake off when drive is in run mode. We do this with a drive output for control and we use a DC supply for the brake. How about that!
Old 11-05-2010, 07:00 PM   #9
Not good, what is the supply to the brake, most are line voltage, so you need a relay, the digital outputs on the drive have a low current limit I think like 200mA, so the in rush of the coil can make the output fail using the form C relay is better because you can do 5A threw the relay which is closer to handle the inrush of a coil. Why is it you choose to question response? I have been using delta drives for better than 10 years.
Old 11-06-2010, 11:51 AM   #10
He said it was a DC brake motor. Now what would you have assumed the brake was?
Look, if you quit being so complicated, I said exactly what you said, I just used fewer words on purpose. Just for you.
Old 11-06-2010, 02:55 PM   #11
Don't need fewer words for me, I understand the process and hardware, if he uses a digital out like you are saying he will burn up the output. I have been doing industrial automation for 20+ years, and have engineered several applications for many processes, so you need not to be so rude as if you know better than anyone, I thought this forum was something everyone could learn from each others experiences, but it seems it's a pissing contest when amateurs as yourself try to act as if you know, show respect and stop being an asshole
Tags
2-wire, 3-wire, dc brake, vfd
Lutron Electronics support is amazing Electric_Light Lighting Design 7 07-17-2010 04:19 PM
Electronics Problems Obsessedgamer420 General Electrical Discussion 18 04-26-2010 05:54 PM
Career Change to Electrician or Electronics technician NickL1975 Introductions 2 02-09-2009 10:44 PM
Delta-delta Transformer Voltage Problems ROMANATOR General Electrical Discussion 3 10-26-2007 12:38 PM