How does a internal motor overload work? - Electrician Talk - Professional Electrical Contractors Forum
Old 10-24-2010, 02:47 PM   #1
Rewards Points: 2,000
Default How does a internal motor overload work?
Neighbor has a 2HP 115volt motor that the internal overload has failed on. Was thinking of putting a external overload on it but was trying to figure out what the three wires going to the internal overload do. It's been a week since I looked at this thing. Seems like one was the neutral but am unsure how it works with the other two leads.
Old 10-24-2010, 02:58 PM   #2
evil bastard
mcclary's electrical's Avatar
Rewards Points: 746
You have a common and a NC, NO.
Most only have a NC.
See exhibit 430.9 in handbook
jwjrw (10-24-2010)
Old 10-24-2010, 03:11 PM   #3
The picture is kinda hard to make out. Instead of that fancy pic they could have used a small wiring diagram. I can't quite make out how it works.
Old 10-24-2010, 04:10 PM   #4
Electric Al
oldtimer's Avatar
Rewards Points: 2,306
Neighbor has a 2HP 115volt motor that the internal overload has failed on. Was thinking of putting a external overload on it but was trying to figure out what the three wires going to the internal overload do. It's been a week since I looked at this thing. Seems like one was the NEUTRAL but am unsure how it works with the other two leads.
Why would it need a neutral ?
Old 10-24-2010, 05:22 PM   #5
Here's my calcs for overloads and conductors at 120 volts:
30amp conductor
30amp over loads based off FLC of 24
60 amp breaker
Motor specs are 2HP, 120/240, FLA is 22 on it I think. It's an air compressor. Seems it was probably wired for 240 volt from the factory. Thing has been modified some.
Old 10-24-2010, 05:23 PM   #6
Because it's wired for 120 volts right now...
Old 10-24-2010, 05:25 PM   #7
Rewards Points: 2,050
I don't know.
Why do some thermal protectors in recessed lighting use a neutral?
Old 10-24-2010, 05:27 PM   #8
Electric Al
oldtimer's Avatar
I M O, the overload is a switch, that's why I asked if it needs a neutral.
Old 10-24-2010, 06:41 PM   #9
Rewards Points: 346
Most of them operate the same way an external O/L does. Excess current causes a bi-metal contact to open.
If it has failed closed, an external O/L can be installed, and the motor is protected.
If it has failed open, you'll have to get at the O/L. Some are mounted inside the motor, some in the terminal box.
Usually, there are 3 terminals on a dual-voltage O/L. One of them goes to a winding (if it were labeled, it'd be T1), the other two go to the terminal box. They're usually labeled P1 and P2.
Cut the leads from the O/L, get rid of the two that went to the terminal box, and extend the winding lead to the box. Label it T1. You now have the factory version of the motor when it is supplied without O/L protection.
The 115 volt connection is now L1 = T1, T3, T5, and L2 = T2, T4, T8 for CW rotation facing the non-drive end; or L1 = T1, T3, T8, and L2 = T2, T4, T5 for CCW.
The external O/L is sized to the nameplate current.
Rob
The Following 3 Users Say Thank You to micromind For This Useful Post:
jwjrw (10-25-2010), nitro71 (10-25-2010), oldtimer (10-24-2010)
Old 10-24-2010, 06:50 PM   #10
I checked it out today. Looks to me what happens is the common is switched. Three leads goto the overload, common coming in, common going to the motor and a motor lead coming off the windings.
Common coming in is on one side of the over load. Other side goes to motor. Then the motor lead connects to a heater that then connects to the motor side common. When it over heats it opens the common. At least I think the lead is the common. Glanced at it for a minute. Interesting.
Old 10-24-2010, 08:15 PM   #11
Rewards Points: 346
The O/L is a two-pole device. Only P1 to the winding (P1) has a heater. P2 is just a switch from P1.
The reason is because current is sensed on T1; it'll be the same regardless of voltage connection.
If the motor is connected for 230, it is a series connection, and the O/L only needs to sense current on P1/T1 and break it if overloaded.
If it's connected for 115, the windings are parallel. Current is the same in both windings, but only one is sensed. Both windings must be de-energized during an O/L. This is why P2 is not used for 230 but is connected to the other winding (T3) on 115.
Rob
Old 10-25-2010, 12:11 AM   #12
I'm getting closer to understanding this. Found a couple of diagrams online but they are a little unclear. I'm on the precipice of figuring it out.
Old 10-25-2010, 12:29 AM   #13
Rewards Points: 2,012
Isn't it just a thermal cutout, like a bimetallic switch? Resets on a temperature drop?
miller_elex is offline   Reply With Quote
Old 10-25-2010, 12:32 AM   #14
Jlarson's Avatar
Rewards Points: 2,792
Yeah probably, just bypass it and throw an OL relay on it and all should be good to go, it will probably take a little reverse engineering to pull it off but it shouldn't be a big deal.
Old 10-25-2010, 03:45 AM   #15
etb
Rewards Points: 250
Last ones I put up were still two wire, but ceiling fans now have a three-wire black box: in series with the light kit and a neutral. They sense current and drive a relay to kill the lights if somebody installs bulbs that pull more amps than should be pulled by (#bulbs)*(max watts). May be a similar thing; would be easy to check.
etb is offline   Reply With Quote
Old 10-25-2010, 02:12 PM   #16
Close, but it stays open till you manually push it closed. Anyone have a good motor diagram showing a single phase 115/230, capacitor start motor with a internal overload?
Here's what I have so far:
http://s95.photobucket.com/albums/l1...t=Motor002.jpg
http://www.owwm.com/files/PDF/FAQ/ElectricMotors.pdf
Old 10-25-2010, 02:16 PM   #17
Thanks Micro for that excellent description. I might have to abduct this air compressor for a few days.
Based off the nameplate data it needs 30 amp overloads, 30 amp wire, and a 60 amp breaker at 120volts. But it comes on a residential style air compressor that wasn't ever wired for that. Wondering if the manufacturer tested it and it doesn't draw that type of load..
motor internal therm.switch spec grade PLCs, VFDs, Motors and Controls 10 04-28-2014 10:22 PM
Motor Overload Question AMPED Commercial Electrical Forum 4 05-05-2010 11:25 AM
Motor Overload speedtronic General Electrical Discussion 3 07-30-2009 09:27 PM
Thermal overload tripping on a motor? ToddH General Electrical Discussion 8 07-04-2009 03:31 PM
can a 200 mA speed control motor overload? theripley General Electrical Discussion 1 01-09-2009 11:45 AM