Default one circuit or two?

I don't do a lot of motor work, so forgive me if this is a 101 question. I have a setup that has two pump motors that will be used alternately through the use of a sequencer. The loads are small (3 A@ 480 v)) and will be protected by individual overload protection. Can I power the two motors with one circuit or do I need a circuit for each?

__________________
A professional in an amateur world.
goose134 is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectricianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!
Old 09-23-2011, 08:57 AM   #2
Heavily Armed Member
 
HARRY304E's Avatar
 
Join Date: Sep 2010
Location: Fascistchusetts
Posts: 29,447
Default

Quote:
Originally Posted by goose134 View Post
I don't do a lot of motor work, so forgive me if this is a 101 question. I have a setup that has two pump motors that will be used alternately through the use of a sequencer. The loads are small (3 A@ 480 v)) and will be protected by individual overload protection. Can I power the two motors with one circuit or do I need a circuit for each?
You only need one circuit because they are only 3 amps and they will not be running at the same time.

And even if they were that's only a 6 Amp load.

HARRY304E is offline   Reply With Quote
Old 09-23-2011, 09:15 AM   #3
I void warranties
 
Jlarson's Avatar
 
Join Date: Jun 2009
Location: AZ
Posts: 10,849
Default

I don't see anything there that would make it so you couldn't put both on the same branch circuit.



Although If its a critical app putting them on one circuit could come back to bite of one motor shorts and trips the breaker.
__________________
The best never stop learning.

Jlarson is offline   Reply With Quote
Old 09-23-2011, 09:18 AM   #4
Member
 
Join Date: May 2010
Location: Arco, Idaho
Posts: 89
Default

Perfectly legal, size the wire at 125% of the largest motor plus the other motor. Do it all the time.
alpha3236 is offline   Reply With Quote
Old 09-23-2011, 01:53 PM   #5
Senior Member
 
goose134's Avatar
 
Join Date: Nov 2007
Location: Chicago
Posts: 1,037
Default

Good point about the critical load. I think in a different case I'd put them on seperate circuits just for a bit more certainty. This is pumps for a air conditioning setup. I didn't think it would be a problem, but I wanted to find out from guys who knew much more than me. Thanks again.
__________________
A professional in an amateur world.
goose134 is offline   Reply With Quote
Old 09-23-2011, 01:55 PM   #6
BBQ
Senior Member
 
BBQ's Avatar
 
Join Date: Nov 2010
Location: New England
Posts: 23,805
Default

220.60 Noncoincident Loads. Where it is unlikely that
two or more noncoincident loads will be in use simultaneously,
it shall be permissible to use only the largest
load(s) that will be used at one time for calculating the total
load of a feeder or service.
BBQ is offline   Reply With Quote
Old 09-23-2011, 02:27 PM   #7
Senior Member
 
Join Date: Jan 2011
Location: canada
Posts: 443
Default

Quote:
Originally Posted by alpha3236 View Post
Perfectly legal, size the wire at 125% of the largest motor plus the other motor. Do it all the time.
that rule is ok but don't use smaller than 14 awg

you can even use only one overload protection for the 2 motors if the contactors for the 2 motors are interlocked (similar to a reversible contactor) since only one will run

Last edited by oliquir; 09-23-2011 at 02:29 PM.
oliquir is offline   Reply With Quote
Old 09-23-2011, 06:37 PM   #8
Senior Member
 
goose134's Avatar
 
Join Date: Nov 2007
Location: Chicago
Posts: 1,037
Default

Bob brings up an interesting point. I'm not 100% sure of the circuit logic, but I think it's designed to run the pumps as alternates. I do know that the sequencer allows for an operation that would ramp one down while running the other up. Now I'm pulling#10 THHN but if the logic is set in the way I just described, would it be a violation?

__________________
A professional in an amateur world.
goose134 is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
How to Know if you have a 20 amp circuit? kage65 General Electrical Discussion 10 03-22-2011 03:50 PM
need a new circuit ampman General Electrical Discussion 21 01-26-2011 07:28 PM
6 Drops per 15 A circuit/8 Drops per 20 A circuit. Whats your opinion? romexrocket NEC Code Forum 32 06-11-2010 06:38 AM