Old 02-28-2009, 08:12 PM   #1
Default siemens SIMATIC S7-300 PLC help please
Have taken a look at a machine with the above PLC, not being familiar, find myself at a loss.
The machine operates correctly but the display performs startup, does not show parameter data, from what I can gather the OP should show connection error on startup if disconnected.
no errors shown- even without connection.
Provided the data cable is present-on power on it should proceed to upload data to OP-from what little info I have.
testing the original cable I found a dead connection on the RS 485 serial connector-repaired and tests out okay.
red / green now have continuity.(only two cores and a 24 v dc connection)
For some reason we do not get expected startup error and the OP shows #### values.
The PLC itself and machine controls work perfectly.
Can enyone tell me if it could have an engineer / tamper parameter?
Lastly we have limited access due to unknown password and the chap who originally installed it did not speak English so any manuals or notes left are in German
sparkie is offline   Reply With Quote
Old 02-28-2009, 10:36 PM   #2
ROMEX_ICAN
p_logix's Avatar
If you are not seeing parameter data i would suggest going online serially or ethernet which ever is available and taking a look at your communications settings.
You say you repaired the RS485 cable. Is that a direct serial connection to a HMI or is the RS485 converted to Ethernet and then the information is written out to the operator workstation?
Did you reboot the HMI after repairing cable?
In the HMI can you look at the communication settings and network settings and make sure they are matched with the PLC.
p_logix
"Meggers Don't Lie, Electricians Lie". Go LAKERS!!!!
p_logix is offline   Reply With Quote
Old 03-01-2009, 05:36 AM   #3
The machine has a rs485 cable which is straight serial over about a 4 meter run, the cable is the correct twin core shielded spec.
Before any repair to the cable was performed the machine had been powered down overnight, with a tester on both ends of the cable I found it to be faulty.
So after repairing it I restarted the machine and the panel fired up with it's usual startup, as we don't have the password for it we can't enter many of the options displayed on the panel.
We really could do with an installation manual and I guess that we would need a
RS232 – MPI / PPI adapter and step 7 lite ?
Old 03-01-2009, 02:08 PM   #4
The manufacturer can give you a password to access all functions. A lost password is no issue as all PLC manufaturers have the generic password. How many characters are in the password. Seems like manufactures like the digit #9. Try 9999.
Old 03-01-2009, 11:54 PM   #5
ROMEX_ICAN
p_logix's Avatar
Here are the passwords for the first 2 level
This is straight from the manual. I'm not sure if you have them or if they will work. Not sure if all this applies to your situation, but here is some info for ya.
3.1.1 Access levels
User class
The SIJECT 15/16 implements a user class concept to enable certain
data areas. The user classes have protection level 1 and 2.
User class 1
When setting the parameters via operator panel, the screen will display
“Enter Password, XXXX”. User should enter the password of class 1.
Factory setting for the password class 1 is 1111. Then push the Enter
key to confirm the entry.
After Switch-On of control system, if there is no action for 5 minutes, the
system will require password entry for the second time when you operate
again.
User class 2
User class 2 requires the password 2 (2000) on the Service screen. It is
set up so as to avoid the accidental modification of function parameters
by the operator. They are the most important parameters with the
influence on the machine function. Only the service engineer has the
accessible right.
3.1 General
Start-up
requirements The following is required:
User Manual: Operation Manual SIJECT 15/16
PC/PG: Data exchange with control system
- With RS232 adapter and SIMATIC S7-300 programming tool:
for down-/upload PLC-program for SIJECT15
With MPI adapter and SIMATIC S7-300 programming tool:
for down-/upload PLC-program for SIJECT16
- With SIJECT adapter and Toolbox:
for updating system software
MMC card: can be used to transfer customer specific picture, recipe
data and PLC-program
If the CPU does not have a battery, the MMC is for the CPU to be in operation.
CPU will go to stop mode if the MMC is remove.
The system configuration hardware configuration + program + network configuration is stored in the MMC card.
If you insert MMC to another CPU and power up the first action is all the data is loaded from the MMC to the CPU.
Thus the CPU will also be password protected.
In future even all the comments will be save in the MMC thus all documentation will be store digitally.
The password is in the MMC as well
as the CPU.
Hope this info helps,
p_logix
p_logix
Old 03-04-2009, 05:28 AM   #6
InControl's Avatar
It sure sounds like you have a profibus cable to me, not RS485.
If it worked before, and now it doesn't, I would cut back and re-terminate both ends. Make sure the shield makes a good connection inside the connector.
Also, assuming its profibus, see if there is a terminator switch on the back of the connectors. The last device on a profibus network should have the switch 'on'.
InControl is offline   Reply With Quote
Old 01-27-2010, 08:42 AM   #7
dear
let's restart whole system with the order of 1st master device i.e. PLC after HMI and don;t invoke the start-up routine, let's give time gape between PLC and HMI , also wait for HMI start-up routine , write to if you face any interruption during this,
side by side make a complete drawing with soft code or parameter for both end , mention each and every thing there ,
i hope you work in hardware side of the system so, don't worries about the inside change
other wise you need system software ( step-7 , PPI CABLE, system PC)
i hope this will help out
-near
acercompaq is offline   Reply With Quote
Old 01-28-2010, 07:57 AM   #8
Is it a Siemens HMI or something else. If it is a Siemens HMI are you running winn cc flex? The tag data could be corrupt, or it could be an addressing problem. You will need to connect to the PLC to check the connections. If your program is in german the word for connections is verbindugun.
Sawdust454 is offline   Reply With Quote
Old 01-29-2010, 09:30 AM   #9
unfortunately the PLC would not respond to either our cable and software or Manufacturers service kit. Appears to be an issue encountered before and replaced FOC
Old 01-29-2010, 01:53 PM   #10
dear sparkie
you need direct and immediate support , you can chat with me,
i have lots of book , manuals, references, but all in big megabytes i can not upload all here
1. search online manual download and read how to secure / save the original software / program on both side in plc side yourmachine.mwl and in hmi side yourmachine.hmi
2. try to find out the machine manufacture (not siemens) and ask the same software ( yourmachine.mwl + yourmachine.hmi )
actually we don't have an idea what kind of tool you have right now to coupe this situation ... i mean (hardware + software)
thanks
best regards
Old 02-08-2010, 10:29 AM   #11
Hi! First Backup your HMI before do something.
Buy or lend S7 MPI Cable to connect your PC and use WinCC to Backup your HMI.
Then search for original Open/Close Loop project and reload again, using step 7 and WinCC integration.
The Siject come generaly with a backup for the HMI and PLC Runtimes and Programs.
Please Post complete Siject model, HMI, cables, etc.
Agamenon is offline   Reply With Quote
what else fits in a siemens panel jjdrees General Electrical Discussion 26 06-03-2009 12:06 PM
Siemens panel problem jack davis General Electrical Discussion 2 02-24-2009 08:21 PM
Siemens Soft Starter Theory DennisR General Electrical Discussion 14 09-07-2008 10:26 PM
i need help with a 14 ds siemens mag starter mission pools Off Topic 9 02-14-2008 09:39 PM
FS- Siemens Sentron Series 600 AMP Circuit Breaker KC_Timbo General Electrical Discussion 1 10-25-2007 05:23 PM