Originally Posted by John Valdes
Sounds like nonsense to me. Who got management on board? You do not check contacts or PM contacts. It's silly. Contacts are either NO or NC. How do you go through a plant full of relays and perform this PM. Do you really think this will save downtime? Good troubleshooting skills are whats in order, not measuring MV's across a contact. Why MV's? Where do you get the MV supply to do the testing. Your multimeter can only measure MV's, not produce them.
Those electricians that will not participate. They most likely realize you are wasting time and money as I do.
Voltage drop is measured across the contacts with the meter set on mV scale. This needs to be done on a live circuit with voltage/current flowing across the contacts. A lower voltage drop indicates low contact resistance. The higher the contact resistance, the hotter the contact surfaces get and the more likely they are to arc out. For example, we measure voltage drop all the time on our cable and conduit fittings. The UL 514B specification requires a fitting to be connected to a 30A DC load and have no more than 15 mV drop across the fitting when the power supply is connected to the box and to the cable or conduit.
It seems that in the OP's case, his equipment is sensitive enough to notice voltage drop, which would be a great application for an SSR or Mercury Relay. I am also assuming that proper troubleshooting is being done when a failure of a relay is analyzed. More often than not, the problem has little to do with a standard cube relay and more with the signal (limit or proximity) switches or other circuit components.
Personally, I find it unusual for control relays to have contact problems unless they have millions of cycles at the rated load (typically 10A). However, Contactors are notorious for burning through contacts depending on the type of motor load and initial draw amps.