Electrician Talk - Professional Electrical Contractors Forum
CLICK HERE AND JOIN OUR COMMUNITY TODAY...IT'S FREE!
Go Back   Electrician Talk - Professional Electrical Contractors Forum > Electrical Trade Topics > PLCs, VFDs, Motors and Controls

Reply
 
Thread Tools Search this Thread Display Modes
Old 09-25-2009, 02:24 PM   #21
Junior Member
 
Join Date: Sep 2009
Location: UK Wales
Posts: 4
Default VFD help

Go for an ABB acs800 75KW. They dont do a 55kw anymore. They pack the 75KW into the 55 frame size. I have just been quoted an unbelievable price for one.

At 75kw the line reactor comes with it.

They will also get massive energy savings if you are controlling centrifugal pumps. ABB have patented DTC which gives very accurate control if you require it.

I have just installed schneider 75kw as a freebee. Line reactor is separate.Its a hell of a lump. Not powered it up yet though i will let you know how easy it is to configure.

yindavies is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectrcianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!
Old 09-25-2009, 09:18 PM   #22
Senior Member
 
Join Date: Nov 2008
Location: east coast
Posts: 123
Default

The VFD would be a good idea however a regular motor will not last on a VFD . A VFD rated motor is designed to tolerate the spiked and high yoltages that a VFD puts out. It is not uncommon for a 480 volt drive to put out 800 + volts. Anouther thing is the distance between the VFD and the motor If it is 100+ feet the wire insulation between the drive and motor become a issue. It is not a plug and play type situation.
LC

Last edited by Lone Crapshooter; 09-26-2009 at 07:46 AM.
Lone Crapshooter is offline   Reply With Quote
Old 09-25-2009, 10:24 PM   #23
Member
 
InControl's Avatar
 
Join Date: Mar 2007
Location: NY
Posts: 91
Default

Quote:
Originally Posted by lukejenson View Post
Even tho it says KSB on the nameplate, it looks like a lenze nameplate to me.
Its the European standard for nameplates. They all look the same.
InControl is offline   Reply With Quote
Old 09-26-2009, 01:04 AM   #24
Junior Member
 
Join Date: Sep 2009
Location: UK Wales
Posts: 4
Default

I agree about the old motors not being invertor rated. Can you purchase new high efficiency motors. If you run these pumps on pressure control as stated the payback is huge.

KSB are a pumps manufacturer. They will tell you if the motor is rated for the job.

I would only be concerned if the motor is over 100m from the drive. You can fit a du/dvt filter if longer.
yindavies is offline   Reply With Quote
Old 11-02-2009, 03:18 AM   #25
Junior Member
 
Join Date: Jul 2009
Location: China
Posts: 6
Default

Quote:
Originally Posted by browningwgm View Post
Hello,

A little background on myself. I'm an active duty HVAC tech serving in USAF. I'm currently deployed to a location in Southwest Asia. I have been asked to look at an issue with a water distribution system. They have 8 45KW (60HP) pumps that are delta wound running 415 VAC 3 ph 50hz. There's 6 power leads going to the motor.

Motor data plate states
400 Delta 50hz
690 Wye 50hz

460 delta 60hz

What I want to know is, can this motor be ran off a VFD? The current setup uses 3 contactors. At startup, the start and shorting contactors pull in. After a couple seconds, the shorting contactor drops out and at the same time the run contactor will pull in. This seems to be a pretty standard start sequence that I've seen on some larger chiller units before.

My goal is to run these pumps off a VFD to avoid constant start/stops that's occuring and wearing out our equipment.

If you need more info, please let me know and I can get it. Any help would be appreciated. Thanks.
run off? sorry. I don't understand.

Motor soft starter may be a choice
acdrive is offline   Reply With Quote
Old 11-02-2009, 05:19 PM   #26
Junior Member
 
Join Date: Sep 2009
Location: UK Wales
Posts: 4
Default

Hi. I am not sure what the shorting contacting is doing. But because you have 6 leads going to the motor I will assume you are using a star/delta starting method.

You can run most 3 phase motors with a VFD but if they are not invertor rated they could fail after a period with insulation breakdown or bearing failure. When ever possible I will fit a new motor with a non drive end insulated bearing. All depends on the application and wether you can afford the motor failure. Another thing is cable lengths and harmonics. Dont want to put you off but you need to be aware of these if you put allot of VFD,s on a network. These are small motors and I will assume cable lengths of less than 100m so you should be ok. Pay particular attention to earthing the motor and VFD.

I would not look at a soft start unless the customer demands one. When you have a VFD installed it is so flexible. You can run half speed, pressure control, level control basically its up to you how you control the water system. I would like to know what it is though as I may be able to offer more advise.

Basically disconnect the shorting and run contactor and connect the out going start contactor cables directly to the power VFD input and then VFD output directly to the motor. Connect the motor in delta at the motor. Now when start contactor energises it will put juice onto the VFD. You can either configure the VFD to run on start up or use a separate run relay. Like I said not sure what your application is. But using a VFD you can put a very slow ramp rate to protect equipment if so desired.

Try to use the VFD start interlock and connect it to an early break contact on the motor local isolator. This is good practise. Stops should not have changed as you have not altered the original start stop circuit.

Hope this helps.
yindavies is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Top of Page | View New Posts

All times are GMT -4. The time now is 01:36 AM.


Electrician Talk © 2006 - 2009 The Building Network LLC