08-30-2009, 09:17 PM
#21
Licensed Pro
Btw, got any pictures of that massive service head with all the conductors pouring out of it?
08-30-2009, 09:46 PM
#22
I have one for you. Made by a sheet metal shop:
08-30-2009, 09:49 PM
#23
Not Peter D
I'm guessing this was a mill or similar building that was decomissioned, and the power needs are just to keep a few lights and receptacles live now...so the poco downsized the service.
Is this corner grounded delta?
08-30-2009, 09:51 PM
#24
Unlimited Lic.Electrician
Did it have a 3rd party label on that weather head?
08-30-2009, 09:53 PM
#25
No, nor is it required to. It was made in a UL panel shop, so it could have had one. Probably would have added a few bucks for a sticker.
08-30-2009, 09:54 PM
#26
No. Condo conversion. The w/h is new. It was temp'd in with the old drop, since there wasn't much going on inside yet.
08-30-2009, 09:59 PM
#27
Not Peter D
Ah right. So you installed that monstrosity?  I'm surprised the poco allowed overhead for a service that large. Clearly there are extenuating circumstances for its existence.
08-31-2009, 09:30 AM
#28
Licensed Pro
Right, that was my point that they you can't go down to the local Cooper Electric Supply and buy a service head for 6 SEC's.
09-01-2009, 04:03 AM
#29
09-01-2009, 04:08 AM
#30
Grandfather is a scary old fire hazard. but, work with what you got! make sure they understand existing, right?
09-02-2009, 09:41 PM
#31
We ended up running 600 alu up the mast in the same 3 1/2" pipe, but they failed it again because my house was originally rated for a 180 amp service with a piece of #4 copper as the ground conductor to the ground rod. I forgot to resize it for the 600 up the mast, so I went back again and sized it correctly to 1/0 Copper (My fault I honestly just forgot it). Then he failed it again saying I needed 24 feet to the top of the weatherhead and that 600 needs a larger size conduit??? 24'? 600 doesn't use 40% pipe fill in a 3" pipe, let alone a 3.5". I'm seriously done messing with it...I'm going to rip if off, replace the vinyl and run it underground, let the poco mess with the wire...
I didn't run 3/0 copper up the mast because the power company said they wouldn't hook to it. The inspector said it was fine but they are two completely seperate things. I don't know how it works for some of the other states but even if it passes the county/city inspector here the power company can still turn it down...
He won't give me an actual piece of paper saying what he wants and why it failed...normally a red card says exactley what's wrong but apparently that's not the case here.
Reason: no damned inspection slip
09-03-2009, 12:02 AM
#32
have you tried to go over his head and talk to the chief inspector? I've had good experiences with mine. He has the power to make an exception.
09-03-2009, 12:06 AM
#33
sorry... I read that fast. Call the head of your poco engineers and see what he says. Same deal, he can make an exception. by the way, his name is sir.
09-03-2009, 12:09 AM
#34
my poco is the same evidently, they can turn down a hook up that is within code beacause the engineer can't figure something out.
09-04-2009, 10:49 AM
#35
Perhaps he forgot that to the rod never needs to be larger than #6?