I usually install #6 feeders for a hot tub with a 50 amp rating but I cant figure out why. Can I use# 8 thhn . if not why. I have never clamped a hot tub drawing more than 30 A thats with all pumps and heaters on. referances please
Thanks
04-29-2010, 03:36 PM
not THAT old!
If it asks for 50 amp. Install 50 amp and # 6 feeders or your warranty will be void.
04-29-2010, 05:55 PM
Chairman of the Bored
Thanks
you need to remember the spike in current when that motor starts to wind up.
I'd rather be sleeping.
04-29-2010, 05:57 PM
Chief Electron Relocator
Originally Posted by Electric Al
If it asks for 50 amp.........
50 amp what? Minimum branch circuit rating, or over-current protection, or both?
Look on the nameplate for MCA and OCD ratings.
04-29-2010, 10:33 PM
Master Plumber
Since we are on the subject - is it required to pull a full size ground for a 50A spa circuit, or can I run a #10 ground?
~Matt
Poor planning on your part does not constitute an emergency on my part.
04-29-2010, 10:44 PM
Heel I'd think a #12 might suffice but I'd go with #10
04-30-2010, 12:28 AM
If you have 75 degree terminals and 75 degree conductor you can use #8 copper @ 50 amps. Remember that NM cable must be sized to 60 degree temperature rating so you can not use #8 if using NM cable. If equipment instructions state #6 minimum then you also cannot use #8.
04-30-2010, 07:07 AM
Many tub manufacturers spec that a full size egc must be used. I believe it is worded to say that the egc must be the same size as the ungrounded conductors.
I have given up using nm cable and now I run conduit so that the egc is not an issue.
04-30-2010, 07:08 AM
Buzz how could #12 suffice? Check Table 250.122 for EGC-- it is based on the breaker size.
04-30-2010, 08:22 AM
I said "I think" it would suffice. What do I know? Enough to use #10, though. It's a pretty simple question with a pretty simple solution: check the code book. I'd be interested to see test results of how well certain size wires carry the fault current before disintegrating.
04-30-2010, 10:00 PM
sizing equipment ground conductors is not about sizing them to prevent the ground wire from overheating it about sizing it large enough to lower its impedance enough to operate the overcurrent device quickly.
04-30-2010, 10:37 PM
PGW Professional
~Matt
That would depend on both 110.3(B) and Table 250.122.
05-01-2010, 12:00 AM
Circumcised Member
~Matt
Only if the power used for the spa is from a transformer or other seperately derived system.
I think.
05-01-2010, 04:15 AM
Master Plumber
Thanks, but I knew this part - it was post 8 from dennis I was unsure about. I am thinking it would be wise to just run a full size EGC to the spa disco. Unless I can check out the specific spa before I get the line ran.
~Matt
05-01-2010, 09:46 AM
~Matt
I think.
I don't know of any requirement like this and I fail to see any logic as to why that would be a requirement.
Voltage (assuming an unlimited capacity in the supply) and impedance of the circuit are the same no matter what the source is. So why should you need a different size conductor on one vs the other?
If anything the SDS will likely have higher impedance and lower available current so you would want the larger conductor on it to allow more current to flow during a fault to allow faster operation of overcurrent device.
05-01-2010, 09:50 AM
Fried Bologna um um good!
Some of the hot tubs I have done said to use #6 in the instructions.
05-02-2010, 09:10 AM
then you must follow them instructions, if not in the instructions then follow NEC.
05-02-2010, 09:17 AM
#18
I think.
It would be good to back this up with an article number. Never heard of it before.
05-02-2010, 09:27 AM
#19
Thats why I said some say to use #6.
05-02-2010, 09:37 AM
#20
I think.
The only thing I find like this is 680.25 (B)(1) but it is in 680 part II for feeders for permanently installed pools and does not apply to hot tubs.
The only parts of 680 that apply to hot tubs and spas are Part I general and part IV spas and hot tubs