Old 03-09-2009, 09:13 PM   #1
switchleg's Avatar
Default backfeeding voltage??
This is the second time that I have run into this situation.
I open the panel (residential) and take voltage readings on all the breakers while they are turned off. One of the breakers reads 120 to ground. Take wire off of breaker and still get a reading of 120v. Second time this happened to me I was only getting a reading of 53v or something like that. Anyone seen this before?
switchleg is offline   Reply With Quote
Old 03-09-2009, 09:24 PM   #2
You're using a DMM, right?
Use a Wiggy and tell me what you get.
I'm an electrician, not a magician.
Old 03-09-2009, 10:15 PM   #3
If all the breakers are off how can you be getting 120 v on the wire. Sounds like this is possibly fed from another panel.
Is the entire house off and you get 120V or do are you turning them off one at a time?
The 53V sounds like a bad neutral but need more info.
Alice
Old 03-09-2009, 10:27 PM   #4
Use a coil or analog meter.
If it's still there charge 3Xs normal to punish the homeowner for saving a buck.
Really low voltage Arc Angle Off Topic 4 02-24-2009 08:22 PM
Low Voltage/ High Voltage MikeD NEC Code Forum 18 02-19-2009 05:17 PM
high voltage low voltage dain Other Codes and Standards 2 02-10-2009 10:12 PM
Low Voltage/ High Voltage MikeD Structured Wiring 1 07-09-2008 04:49 PM
Line voltage and low voltage makita1 Structured Wiring 1 03-27-2008 07:06 PM