Originally Posted by raswinde
which is best a 320 amp service of a so-called 400 amp service for a single family dwelling, i don't think that there is a 400 amp service for a house!! is there??
There are few diffrent type of 320 class meter socket and the best advise I will give to you is check with your POCO to see which type they will approve it.
That is the first thing you will need to check with them and they do have approved listing on their regulation book or online format and the other thing the POCO will tell you the meter location some case the reguations will change so keep in your mind it will be the same location maybe not depending if you are on overhead or underground set up.
speaking of true 400 amp service that will come in two diffrent verison depending on what the POCO will say it will be either bolt on 400 meter or CT cabent { my POCO in Wisconsin can use bolt on up to 600 amp both mono et triphase supply but in France anything over 160 amps must have CT'ed }
The other thing you will gasp a min a true single 400 amp load center will cost heck alot more than 2 X 200 amp load centres will be.
Merci,Marc