I,m installing a 34 KW Kohler generator with a 2 inch schedule 89 underground feed that stubs up thru the concrete pad. The nuetral in the transfer switch is not switched so the unit does not require a ground but do i still have to ground the case? I,m pulling 1/0 thhn do i need another green 1/0 or will a # 4 suffice? I always use galvanized and am not familiar with grounding sizes with pvc
greenlee is offline   Reply With Quote
Old 04-30-2012, 07:58 AM   #2
Electrical Simpleton
Pete m.'s Avatar
It will depend on the size of the OCPD in the genset. See 250.122 and table 250.122