Old 04-11-2012, 07:38 PM   #1
Default Two prong to three prong
So, we can install a GFCI receptacle to replace the existing two prong receptacles and load side the remaining and install three prong receptacles. Also, we will need to arc fault the circuit. Has anyone done that with older wiring and not have any arc fault issues?
Old 04-11-2012, 07:56 PM   #2
B W E's Avatar
Why do you have to install an AF breaker? I have not put an AF on older wiring but have heard horror stories
Old 04-11-2012, 08:33 PM   #3
I believe it is a requirement in the 2011 code if you replace two prong with a three prong the circuit must be arc faulted if required. I'll need to pull the code book out tomorrow and verify.
Old 04-11-2012, 08:57 PM   #4
Chief Electron Relocator
210.12(B) Branch Circuit Extensions or Modifications — Dwelling
Units.
In any of the areas specified in 210.12(A), where branch-circuit wiring is modified, replaced, or extended, the branch circuit shall be protected by one of the following:
(1) A listed combination-type AFCI located at the origin of the branch circuit
(2) A listed outlet branch-circuit type AFCI located at the first receptacle outlet of the existing branch circuit.
Chris1971 (04-11-2012)
Old 04-11-2012, 09:22 PM   #5
Chris, I believe all you need is GFCI protection not AFCI protection, AFCI only if you extend the circuit or modify it, if your just changing outlets from 2 prong to 3 prong GFCI is fine, someone chime in if I'm wrong
ohiosparky99 is offline   Reply With Quote
Old 04-11-2012, 09:28 PM   #6
In the 2011 it has changed. The problem is you are looking at the wrong article. Note the Date
406.4(D)(4) Arc-Fault Circuit-Interrupter Protection. Where a receptacle outlet is supplied by a branch circuit that requires arc-fault circuit interrupter protection as specified elsewhere in this Code, a replacement receptacle at this outlet shall be one of the following:
(1) A listed outlet branch circuit type arc-fault circuit interrupter receptacle
(2) A receptacle protected by a listed outlet branch circuit type arc-fault circuit interrupter type receptacle (3) A receptacle protected by a listed combination type arc-fault circuit interrupter type circuit breaker.
This requirement becomes effective January 1, 2014.
Old 04-11-2012, 09:29 PM   #7
Wouldn't changing the receptacles be considered a modification? If so, I believe arc fault would be required.
Old 04-11-2012, 09:30 PM   #8
So yes, arc fault is required.
Old 04-11-2012, 09:31 PM   #9
Look at the last sentence-- the date it is effective
Old 04-11-2012, 09:35 PM   #10
Thanks. I do read most of your posts.
Old 04-11-2012, 09:37 PM   #11
Cletis's Avatar
Default GFCI Breaker
Just GFCI breaker it. I used to try to find the first one on the string and gfci rec. it with all the load off it, but, after much thought it turns out waaaay cheaper to just buy a gfci breaker and protect the whole circuit. You'll save ton's on labor tracing things out and trying to cram gfci rec. in little metal boxes.
Out!
www.cletiselectric.com
Cletis is online now   Reply With Quote
The Following User Says Thank You to Cletis For This Useful Post:
mikeykcl (05-31-2012)
Old 04-11-2012, 09:39 PM   #12
Out!
That was my initial thought until I thought I needed to arc fault them. That isn't the case.
Old 04-11-2012, 09:46 PM   #13
B W E's Avatar
So a receptacle is considered "branch circuit wiring?"
And the 406.4 article talks about circuits that should be arc fault protected. Are existing circuits in 50 year old houses required to be arc fault protected? I still say no arc fault required.
Old 04-11-2012, 09:53 PM   #14
No arc fault until January 2014 if you modify the circuit.
Old 04-11-2012, 10:01 PM   #15
Cletis's Avatar
Default ok
Ok. So, I figure somewhere around 2018 that will become active around here...
Old 04-11-2012, 10:26 PM   #16
B W E's Avatar
How is changing a receptacle modifying the circuit? It says "branch wiring". Will changing a light fixture also require us to put in arc faults? How about a switch?
The Following User Says Thank You to B W E For This Useful Post:
electrictim510 (04-12-2012)
Old 04-12-2012, 03:21 PM   #17
If your changing from two prong to three prong, I would consider that a modification.
Old 04-12-2012, 03:29 PM   #18
B W E's Avatar
How about toggle to dimmer? Chandelier on fan box to fan?
Old 04-12-2012, 03:38 PM   #19
210.12B of the 2011 NEC.
Old 04-12-2012, 03:42 PM   #20
Sometimes if I don't have a gfi breaker I will put a gfi outlet or a dead front gfi at the panel for that circuit.
mnelectrician is offline   Reply With Quote
The Following User Says Thank You to mnelectrician For This Useful Post:
Chris1971 (04-12-2012)
updating Two prong to a three prong receptacle sokoservices Residential Electrical Forum 22 06-21-2011 09:35 AM