Originally Posted by Loose Neutral
Where's the electrical engineer when you need one. I'm simply saying i think the phase difference is derived from the generator and leg A's sine wave goes up and leg B's goes down. But I could be wrong it has been a while since school.
This is where some of the confusion comes in...
There is no sine wave on leg A. In other words, you can't supply voltage with a single wire. Rather, you can measure a sine wave from leg A to leg B, from leg A to neutral, or from leg B to neutral. Note that when measuring the 120V sine wave of a 120/240 split phase system with an O-Scope, one typically places the ground clip on the neutral and the probe on one leg or the other. When moving the probe from leg A to leg B, this results in swapping the left-to-right order of the probes and, therefore the polarity. This is why people tend to think that the two 120V sine waves are 180 degrees out of phase.
Again, if they were 180 degrees out of phase,
1) that would mean that they would cancel each other out.
2) there would have to be more than one transformer, since you can't create more than one sine wave (or phase) with a single transformer.