500 mcm and dual lugs - Electrician Talk - Professional Electrical Contractors Forum
Old 11-06-2010, 11:12 PM   #1
Default 500 mcm and dual lugs
Need some input on Connection on a Commercial Hot Water Boiler. The feed is 480v, 500mcm thhn, breaker for the unit is 400 amp and the draw on the boiler is 325 amps. The lugs on the new heater are only big enough to take a wire about half as big as the 500 mcm. I proposed just splitting the wire apart and putting each half into a lug for that phase. I am now hearing that we need to put in 2 conductors for each phase so that one wire will go to each lug.
BOILERMAKERCSA is offline   Reply With Quote
Old 11-06-2010, 11:14 PM   #2
Rewards Points: 2,050
2 sets of 2/0 copper would do it and have cost less.
You could call the manufacturer and see if they have or will approve different lugs for the unit.
Old 11-06-2010, 11:19 PM   #3
we had planned on using the existing 500 mcm wires
thanks
Old 11-06-2010, 11:24 PM   #4
cdnelectrician's Avatar
Rewards Points: 1,018
Do not split the wire, that is a poor connection and bad workmanship. Change the lugs on the boiler to the proper size or call an electrician .
Old 11-07-2010, 12:14 AM   #5
william1978's Avatar
Rewards Points: 2,000
Old 11-07-2010, 01:26 AM   #6
I wonder if you could use a Polaris connector. Parallel your conductors from the boiler disco to the tap. I really don't know if that would be legitimate.
The Following User Says Thank You to nitro71 For This Useful Post:
brian john (11-07-2010)
Old 11-07-2010, 01:29 AM   #7
Ambassador of Amps
TOOL_5150's Avatar
Rewards Points: 2,114
That's exactly what I was thinking. Anyone got any code references for doing that?
-Matt
I HAVE THE RIGHT TO OFFEND ANYONE I PLEASE. YOU HAVE THE RIGHT TO BE OFFENDED, YOU DO NOT HAVE THE RIGHT TO SHUT ME UP.
Old 11-07-2010, 02:02 AM   #8
Rewards Points: 2,182
eric7379 is online now   Reply With Quote
Old 11-07-2010, 02:16 AM   #9
Mac adapters would probably work
williamj is offline   Reply With Quote
Old 11-07-2010, 07:22 AM   #10
evil bastard
mcclary's electrical's Avatar
Rewards Points: 746
Crimp on a sleeve pin of the correct size
Old 11-07-2010, 07:30 AM   #11
Jlarson's Avatar
Rewards Points: 2,792
I would do one of these two, I would probably go the pin terminal route though just cause it would mean I wouldn't have to deal with the manufacture.
Old 11-07-2010, 07:34 AM   #12
The problem I see is the following
If the manufacturer planed on two sets of say 2/0, 3/0, 4/0 etc. there is a good chance there is not enough wire bending space for 500 Kcmil.
Adding pin terminals will further reduce the bending space and that assumes you could find a pin terminal that would drop the required amount of size and still be rated for 325 amps.
Old 11-07-2010, 07:37 AM   #13
Is a sleeve pin, the same as a ferrel?
They are hard to find for 500's.
Dnkldorf is offline   Reply With Quote
Old 11-07-2010, 07:54 AM   #14
Jlarson's Avatar
Last 500 mcm pin terminals I priced were like $40 each. And I don't remember there being an amp rating on them but that was a while back and little details like that get lost.
Old 11-07-2010, 08:11 AM   #15
Thanks for all the input. It is good to see a lot of valid points and not too much BS. I think we might pull in the new 2/0.. The 500 is already pulled to the unit and bending space is an issue but can be done. I like the idea of the crimp on conn. But gotta get this done today. My lugs unfortunately have 2 holes in the top for the 2/0 and about 16 in the bottom for all my smaller circuits on my heaters and ect. I do follow the logic on not splitting the wire but how much of a difference is it then to put my 2 - 2/0 together on the other end with 2 wires in 1 lug. thanks for all the input.
Old 11-07-2010, 10:37 AM   #16
Rewards Points: 1,106
I'd stick to boiler making. Typical of you guys to hack it in.
Loose Neutral is offline   Reply With Quote
Old 11-07-2010, 11:07 AM   #17
Rewards Points: 150
2/0 would be too small if you plan on pulling 6 ccc in one pipe.
Distribution blocks are cheep and easy to find.
Wingnut is offline   Reply With Quote
Old 11-07-2010, 11:08 AM   #18
That is true.
Old 11-07-2010, 12:17 PM   #19
Rewards Points: 3,855
I've seldom run across one of them that didn't have an issue, long term.
Old 12-03-2010, 10:00 AM   #20
Do not split the wire. The maker of this commercial hot water boiler knows it draws 325 amps, they probably give 2 options dual lugs and single lug. Call them and indicate the 500 MCM already exist and you need thier single lug termination to complete the job to meet the NEC. Throw it back at them.
wayne g is offline   Reply With Quote
neutral lugs ge tm2020 joe cool General Electrical Discussion 30 05-18-2011 07:54 PM
Screws n Lugs Paan Er O General Electrical Discussion 8 04-16-2010 10:05 PM
service panel meterside lugs... Tom Neighbarger Residential Electrical Forum 6 03-04-2010 10:16 PM
One hot, no neutral to main lugs of 120v panel Kharnivour Residential Electrical Forum 2 01-18-2010 02:07 PM
Torque on bolts lugs & terminations nick General Electrical Discussion 43 04-20-2009 10:40 PM