Connected load vs demand load - Electrician Talk - Professional Electrical Contractors Forum
Old 01-08-2012, 11:24 PM   #1
Rewards Points: 25
Default Connected load vs demand load
Hi, my boss is doing a load calc and existing load center schedule. He is using a template an inspector gave to him. It has blanks for connected load and demand load and we need help figuring out the difference. In the sample problem they have different values. Thanks guys
Glennsparky is offline   Reply With Quote
Old 01-08-2012, 11:29 PM   #2
animal lover /rat bastard
wildleg's Avatar
Rewards Points: 404
the connected loads are all the loads that are installed. the demand load is the amount that article 220 says you need to use to do the load calc (different parts of 220 allow you to use a demand for several loads of same type that are not going to be running simultaneously and continuously, depending on the occupancy and the types of loads)
Glennsparky (01-08-2012)
Old 01-09-2012, 10:32 PM   #3
Rewards Points: 2,050
Default peak
you can also do peak demand on occasion based on the highest reading from poco at the property address to overrule your calculated demand sometimes. I did it once to keep an existing 400 amp service instead of having to bump up to a 600 amp. (calc was 408 amps but peak was only 225 amps).
Available Load or Calc Load VD wiremanhelp NEC Code Forum 3 06-27-2011 03:27 AM
load demand, & load meter pimpin electrician General Electrical Discussion 3 05-25-2010 10:49 PM
How to calculate No load current and No load torque in DC Motor AMIanna General Electrical Discussion 3 05-21-2010 09:15 AM
Load Bank Generator Testing vs. Using Building Load to test generators. MR MAB Other Codes and Standards 15 03-16-2009 06:37 PM
Service demand load adranv76 NEC Code Forum 2 04-26-2007 10:30 PM