Old 10-26-2009, 08:28 PM   #61
A really great way to really undrstand exactly what is going on is to look at the sine wave graph in relation to a generator that is producing it. This is truly where the EMF (electromotive force - voltage) is being created. you will see the start points for each phase and there coralation between each other is due to the position of the outgoing conductor and the distance between it and the magnet that is spinning around creating an EMF. You remember the science experiment with the magnet and the lamp cord, well thats how most of our electricity is produced. If you put a little thinking into positioning diffferent magnets and some sort of other force to drive it you can create your own 3 phase generator.
Tyha is offline   Reply With Quote
Old 10-26-2009, 10:30 PM   #62
Originally Posted by InPhase277 View Post
Yes. What Toronto was saying is that most stoves aren't just 240 V. They are 120/240, and require a neutral. So if you have just a straight 240 V delta, then you couldn't use anything that required a neutral. But if you had a 120/240 V delta with a center tap providing a neutral, then it would be fine.
Specifically, the single phase 240 could be used for anything that required it. You will usually find a 120/240 V delta in heavy commercial buildings, like machine or cabinet shops. Very often, table saws are 240 V single phase. Many window unit and through-the-wall A/C units are 240 V single phase.
using delta for contant balanced loads eg single phase or 3 phase heaters more accurate element control. like heat trace or barrel heaters on plastic extrution machinery
sparky105 is offline   Reply With Quote
Old 10-26-2009, 10:50 PM   #63
Rat in a Dress
BCSparkyGirl's Avatar
Please dont get your info from wikipedia. It can be put up there by anyone, and that being said, some douche can put up any info they want nd have people believe it. I never look at that site.
I can drink you pretty.......
BCSparkyGirl is online now   Reply With Quote
Old 10-26-2009, 11:50 PM   #64
That Guy
Mr. Sparkle's Avatar
Hahaha my brother was the drummer for The Who for a few days.
"Whenever you find yourself on the side of the majority, it is time to pause and reflect."
Mark Twain
Mr. Sparkle is online now   Reply With Quote
Old 10-30-2009, 12:48 PM   #65
Yes, it does. But it is just convention that when two of the three phases is used it is called single phase. And when using only two of the three phases, the resulting waveform is that of a single sine wave, a composite of the two.
There seems to be some confusion here. I think you're confusing a "leg" with a "phase." Each phase is produced by a single secondary transformer coil and thus, 2 wires per phase. The 3 secondary transformers are then connected in such a way that only 3 wires are connected to a breaker panel (in either a wye or delta configuration). Tapping off any 2 of the 3 wires is essentially the same as tapping off of only 1 of the 3 secondaries, and thus only a single phase. So the single phase sine wave is not a "composite of the two," rather it is simply just one of the 3 sine waves that make up the 3-phase voltage, depending on which wires were tapped from. It's not "just convention."
Remember that a sine wave (a phase) doesn't exist on a single wire (a leg) by itself. For instance, how do you measure a sine wave with an o-scope? You connect the probe to one point and the ground clip to another ... it takes 2 wires!
zgozvrm is offline   Reply With Quote
Old Yesterday, 12:53 PM   #66
Originally Posted by guitarboyled View Post
The delta configuration with center tap concept seems harder to grasp.
If figure A represents a 120v/208v wye configuration supplying 3 phases at 208v does figure B represent a 3 phase delta configuration with center tap supplying 3 phases at 240v?
So does this mean that with a 120/208v wye system you do not have any more than 208v single phase (A-B, B-C, C-A)? Thanks, Greg
euroah is offline   Reply With Quote
Old Yesterday, 02:45 PM   #67
Yes, 208V is the most you can get.
Phase to phase voltages will all be 208V
Phase to neutral voltages will all be 120V
Can someone please explain... zappy NEC Code Forum 5 04-18-2009 09:38 AM
new service 120/208V 800A 3PH jfwfmt General Electrical Discussion 61 09-19-2008 11:40 AM
Hot Tip on 5th terminal (208V) meters: MDShunk Services and Service Equipment 5 10-04-2007 10:15 AM
How many ways can you explain the reason for saying NO? John General Electrical Discussion 16 03-24-2007 09:52 PM
Someone explain 480 delta 3 phase? rod213 General Electrical Discussion 3 03-17-2007 03:56 AM