feed through lugs - Electrician Talk - Professional Electrical Contractors Forum
Old 11-07-2012, 08:14 AM   #1
Rewards Points: 27
Default feed through lugs
Whats the difference between regular lugs and feed through lugs? oblong shape? In a riser that has feeders from floor to floor instead of bugging the feeders can you put to wires under the panel lugs if there rated??
deanos is offline   Reply With Quote
Old 11-07-2012, 08:19 AM   #2
NRA Member
backstay's Avatar
Rewards Points: 790
Feed through is a term to indicate there are lugs at the bottom of a buss that are connected to the main. So you can have a 200 amp panel with a main, 12 spaces and you can feed out if it at 200 amps. I use these to feed trailer houses.
Old 11-07-2012, 07:56 PM   #3
mbednarik's Avatar
Rewards Points: 1,054
If you have lugs rated for both wires i do not see the problem.
mbednarik is online now   Reply With Quote
Old 11-07-2012, 08:34 PM   #4
Rewards Points: 2,050
Default this
While were talking about feed thru lugs. Say it's a 400 amp panel with feed thru lugs. Can you come out of A and B and neutral and feed these 3 polaris taps with say 4/0Cux2 in each then come out with say 8 #1Cu going to 8 - 100 amp sub panels close by?? Is there a limit other than box fill or amount of sub's off feed thru's ??
Old 11-07-2012, 10:08 PM   #5
RePhase277's Avatar
Rewards Points: 3,106
Is there a limit? Yes. You can't tap a tap.
Old 11-07-2012, 10:19 PM   #6
Default not
it's not really tapping a tap I don't think. We just energizing the whole bar and coming off it 8 times....code ref/ article?
Old 11-07-2012, 10:22 PM   #7
Default C
It's kind of like C-taps which are exempt from tap rules right
372.12
Old 11-07-2012, 10:41 PM   #8
RePhase277's Avatar
372.12
Cellular concrete floor raceways were about the furthest thing from my mind... but I get the idea. I suppose that as long as the ampacity of the first "tap" (at the lugs) is equal to the feeder, then it doesn't count as a tap as defined in 240.2.
Still, I don't know if I'd do it. We wouldn't be allowed to do it stright off a transformer secondary for the reason I stated, so we might as well be consistent even if we tecnically could get away with it.
feed through lugs deanos General Electrical Discussion 0 11-07-2012 08:14 AM
Torqueing lugs Xjourneybenderx General Electrical Discussion 18 06-25-2011 07:57 AM
AL/CU lugs.. B4T General Electrical Discussion 76 12-27-2010 09:22 PM
How to fit 600s on 500 lugs Suncoast Power General Electrical Discussion 96 12-14-2010 07:47 AM
Screws n Lugs Paan Er O General Electrical Discussion 8 04-16-2010 09:05 PM