Old 02-09-2017, 04:23 AM   #1
Senile Member
 
macmikeman's Avatar
 
Join Date: Jan 2007
Location: Honolulu
Posts: 20,308
Rewards Points: 2,954
Default Fire alarm system question

Well,,,,,,, I'm doing a tenant job that has audible sirens, strobing audible sirens, pull gizmo's, stuff like that. Last time I wired up one of these was pretty long ago, like maybe 1987 or so. So ,,, I forget now about the back boxes for the stuff in the typical fire alarm system. My memory says use 4-11/16 boxes for all of it, but I can't remember if it is 1 gang mud rings , two gang , or is it no gang and just bring the box out to the finish? I'm pushed to hustle speed and don't have much time to research. Any input will be most appreciated. Mahalo.
__________________
“That all changes—starting right here and right now.” Jan. 20 “will be remembered as the day the people became the rulers of this nation again.” Donald Trump
macmikeman is online now   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectricianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Sponsored Links
Advertisement
 
Old 02-09-2017, 05:18 AM   #2
Modérateur
 
frenchelectrican's Avatar
 
Join Date: Mar 2007
Location: Philippines { for a while }
Posts: 5,785
Rewards Points: 630
Default

Quote:
Originally Posted by macmikeman View Post
Well,,,,,,, I'm doing a tenant job that has audible sirens, strobing audible sirens, pull gizmo's, stuff like that. Last time I wired up one of these was pretty long ago, like maybe 1987 or so. So ,,, I forget now about the back boxes for the stuff in the typical fire alarm system. My memory says use 4-11/16 boxes for all of it, but I can't remember if it is 1 gang mud rings , two gang , or is it no gang and just bring the box out to the finish? I'm pushed to hustle speed and don't have much time to research. Any input will be most appreciated. Mahalo.
Hey Mac.,,

Yes you can use 4-11/16 or 4 inch box and most audible and strobe units can use two gang mudring on it. but I advise ya use to the deep boxes much as you can and make sure you get them in red box or paint them red.

The pull station .,, Just dont quote me wrong some do take single gang mudring all it depending on what model pull station being used.

The old strobe lights I done before many moons ago was used on 4 inch octagal box so the modern one I bet it can fit on convental two gang box or two gang mudrings it the same with combo units ( sounder and strobe units )

Pay attetion to the mounting heights on those devices they are kinda picky on the location and heights.
MechanicalDVR and telsa like this.
__________________
Bleu est beau.
frenchelectrican is offline   Reply With Quote
Old 02-09-2017, 05:23 AM   #3
Senior Member
 
Join Date: May 2015
Location: Sacramento, California
Posts: 7,187
Rewards Points: 12,650
Default

All of the cable is a pig for space.

It's common for extra-sized boxes.

As in 4s deep PLUS a 4s extension

Having rescued more than a few 'astray' F/A systems...

I'll shut up for now.
telsa is online now   Reply With Quote
Old 02-09-2017, 05:55 AM   #4
Senior Member
 
splatz's Avatar
 
Join Date: May 2015
Location: Parts Unknown
Posts: 2,584
Rewards Points: 1,672
Default

I don't do much of it but be careful I definitely see a lot of cluster f***s on recently installed systems, ugly surface mount boxes with extenders stacked on top and devices on the extenders.

I think the a lot of devices are made to mount directly on a four square box, but not all. I think wiremold alarm device boxes mount on top of a four square.

Garvin makes what looks like a more flexible 5 1/2" surface mount box that accepts different size devices and mounts to give you more flexibility.



I think maybe DEEP four squares even with the finish would probably work for a lot of systems, maybe need the wiremold / garvin to take up the slack if not.
__________________
'You must either conquer and rule or serve and lose, suffer or triumph, be the hammer or the anvil.'
splatz is online now   Reply With Quote
The Following User Says Thank You to splatz For This Useful Post:
telsa (02-11-2017)
Old 02-09-2017, 06:00 AM   #5
motherplucker
 
chicken steve's Avatar
 
Join Date: Mar 2011
Location: the Green Mountain state
Posts: 34,535
Rewards Points: 4,428
Default

FA's became an attachment license in VT about 15 yrs ago w/ceu's etc

~CS~
chicken steve is offline   Reply With Quote
Old 02-09-2017, 07:02 AM   #6
Semper Fidelis
 
Suncoast Power's Avatar
 
Join Date: Jan 2009
Location: Florida
Posts: 13,331
Rewards Points: 4,314
Default

We put deep boxes flush with the finish for horn strobes, 7' or as called out on the plans,
Deep boxes with single gang for the pull stations.

That should get you there.

As for the red paint, we do it just to keep people out of them.
sbrn33 likes this.
Suncoast Power is offline   Reply With Quote
Old 02-09-2017, 08:29 AM   #7
still in business
 
sbrn33's Avatar
 
Join Date: Mar 2007
Location: middle america
Posts: 8,172
Rewards Points: 2,294
Default

Yea, I just use deep 4 sq's with brackets. 2 gangs for strobes, single gang for pull stations and round for detectors. Never once had a problem with over fill, one wire in and one wire out.
You gonna love the new alarm systems,especially if it is addressable.
__________________
I still can't believe you even posted that trash.
sbrn33 is offline   Reply With Quote
The Following User Says Thank You to sbrn33 For This Useful Post:
Suncoast Power (02-09-2017)
Old 02-11-2017, 12:57 AM   #8
Deplorable-Electrician
 
MechanicalDVR's Avatar
 
Join Date: Dec 2007
Location: God's Country of Virginia
Posts: 25,066
Rewards Points: 19,478
Default

Quote:
Originally Posted by telsa View Post
All of the cable is a pig for space.

It's common for extra-sized boxes.

As in 4s deep PLUS a 4s extension

Having rescued more than a few 'astray' F/A systems...

I'll shut up for now.
What do you mean extensions?

telsa likes this.
__________________
DJT, making libtards cry since 20 Jan 2017
MechanicalDVR is online now   Reply With Quote
The Following User Says Thank You to MechanicalDVR For This Useful Post:
telsa (02-11-2017)
Old 02-11-2017, 01:18 AM   #9
Watt Pusher
 
B-Nabs's Avatar
 
Join Date: Jun 2014
Location: Port Coquitlam, Canada
Posts: 1,045
Rewards Points: 436
Default

I would put in just a little time to research your particular system. The different manufacturers are all over the map in terms of how their different devices mount, and how much space they may take up within the back box.
__________________
Is that a real poncho or is that a Sears poncho?
B-Nabs is offline   Reply With Quote
Old 02-11-2017, 07:01 PM   #10
Senior Member
 
Join Date: Nov 2012
Location: Massachusetts
Posts: 124
Rewards Points: 236
Default

Why is everyone suggesting to use or do use extra deep boxes? old Simplex fire alarm equipment is gone . I do alot of fire alarm and I use standard 16,18 or 22 cu in 1-gang plastic box if non mc and 1-1/2" 4 sq with 1-gang ring for pulls and horn strobes and 2-1/8" deep 4sq without ring for flush modules

the IDC or SLC wires will be 18 or 16 ga and NAC cables 16-2 to 12-2 and the devices don't need alot space.
splatz likes this.
farmantenna is offline   Reply With Quote
The Following User Says Thank You to farmantenna For This Useful Post:
splatz (02-11-2017)
Old 02-11-2017, 07:26 PM   #11
Senior Member
 
Signal1's Avatar
 
Join Date: Feb 2016
Location: Boston Area
Posts: 795
Rewards Points: 472
Default

Quote:
Originally Posted by farmantenna View Post
Why is everyone suggesting to use or do use extra deep boxes? old Simplex fire alarm equipment is gone . I do alot of fire alarm and I use standard 16,18 or 22 cu in 1-gang plastic box if non mc and 1-1/2" 4 sq with 1-gang ring for pulls and horn strobes and 2-1/8" deep 4sq without ring for flush modules

the IDC or SLC wires will be 18 or 16 ga and NAC cables 16-2 to 12-2 and the devices don't need alot space.
Agreed. Fire Alarm is my specialty. Everything is a lot smaller now. It's all data now.
Most horn strobes come with with a backplate that pretty much mounts to anything, and the H/S doesn't extend into the box at all.
Attached Images
 
__________________
I can see Bunker Hill from my house!
Signal1 is online now   Reply With Quote
The Following 3 Users Say Thank You to Signal1 For This Useful Post:
360max (02-15-2017), splatz (02-11-2017), telsa (02-15-2017)
Old 02-15-2017, 06:27 PM   #12
Senior Member
 
Join Date: May 2014
Location: Texas
Posts: 216
Rewards Points: 22
Default

Quote:
Originally Posted by Signal1 View Post
Quote:
Originally Posted by farmantenna View Post
Why is everyone suggesting to use or do use extra deep boxes? old Simplex fire alarm equipment is gone . I do alot of fire alarm and I use standard 16,18 or 22 cu in 1-gang plastic box if non mc and 1-1/2" 4 sq with 1-gang ring for pulls and horn strobes and 2-1/8" deep 4sq without ring for flush modules

the IDC or SLC wires will be 18 or 16 ga and NAC cables 16-2 to 12-2 and the devices don't need alot space.
Agreed. Fire Alarm is my specialty. Everything is a lot smaller now. It's all data now.
Most horn strobes come with with a backplate that pretty much mounts to anything, and the H/S doesn't extend into the box at all.
Depends on manufacturer and device. Edwards ceiling mount strobes and speaker/strobes only mount on 4square boxes, and the speaker/strobes stick into the box maybe more than an inch.
Jarp Habib is online now   Reply With Quote
Old 02-15-2017, 07:22 PM   #13
Senior Member
 
Signal1's Avatar
 
Join Date: Feb 2016
Location: Boston Area
Posts: 795
Rewards Points: 472
Default

Quote:
Originally Posted by Jarp Habib View Post
Depends on manufacturer and device. Edwards ceiling mount strobes and speaker/strobes only mount on 4square boxes, and the speaker/strobes stick into the box maybe more than an inch.
I do agree there are many configurations, but my point was that typically you don't need all those deep boxes any more.

Voice evac systems with speakers do need a little more room.
MechanicalDVR and 360max like this.
__________________
I can see Bunker Hill from my house!
Signal1 is online now   Reply With Quote
The Following User Says Thank You to Signal1 For This Useful Post:
360max (02-15-2017)
Old 02-15-2017, 08:36 PM   #14
Watt Pusher
 
B-Nabs's Avatar
 
Join Date: Jun 2014
Location: Port Coquitlam, Canada
Posts: 1,045
Rewards Points: 436
Default

Quote:
Originally Posted by farmantenna View Post
Why is everyone suggesting to use or do use extra deep boxes? old Simplex fire alarm equipment is gone . I do alot of fire alarm and I use standard 16,18 or 22 cu in 1-gang plastic box if non mc and 1-1/2" 4 sq with 1-gang ring for pulls and horn strobes and 2-1/8" deep 4sq without ring for flush modules

the IDC or SLC wires will be 18 or 16 ga and NAC cables 16-2 to 12-2 and the devices don't need alot space.
Quote:
Originally Posted by Signal1 View Post
Agreed. Fire Alarm is my specialty. Everything is a lot smaller now. It's all data now.
Most horn strobes come with with a backplate that pretty much mounts to anything, and the H/S doesn't extend into the box at all.
I just finished wiring an entire apartment building with Simplex speakers, and I can tell you that we needed to use very deep boxes (we went with deep 4x4 with shallow extension because for some reason in Canada 3 1/2" deep 4x4 boxes don't seem to exist). That is why I would recommend anyone installing a fire alarm find out what the devices they are going to be installing will require, so that they don't end up having to do a bunch of work to fix their rough-in, or end up with some hacked together workaround. I agree that most devices these days are much smaller than they used to be. It's just that most ain't all, is all.
MechanicalDVR likes this.
__________________
Is that a real poncho or is that a Sears poncho?
B-Nabs is offline   Reply With Quote
Old 03-14-2017, 12:08 AM   #15
Member
 
Join Date: Nov 2015
Location: Saskatchewan
Posts: 59
Rewards Points: 114
Default

Thread is a month old but I'll throw my two cents in...

I was lucky to be tasked with single handedly doing the FA system of a couple of small buildings (much of it surface mount). Go with deep boxes as many devices have little modules attached to them that gives them a huge ass end. This is what I've found works...

- Pullstations: 2104 or 4x4 deep (preferably) with single gang mud ring. If you're t-tapping and using 18 or 14 awg wire you can get away with an FS box as well.
- Smokes/Heat: deep o
- CO/ smoke co combos: 4x4 deep. some bases will fit a 4-11 as well which is also recommended. The audible CO bases also need extra wires for 24vdc power to them.
- Isolator modules: 2 gang 2104 or 4x4 deep with 2 gang mud ring.
- Strobes: 2104, handy box, FS box.
- EOL and most of the other special modules will fit single gang boxes.
__________________
I said I am an electrician, I never said I was a good one.
Mr.Awesome is offline   Reply With Quote
Old 03-21-2017, 12:52 AM   #16
Member
 
ElectricMetalTuba's Avatar
 
Join Date: Mar 2017
Location: Alberta
Posts: 62
Rewards Points: 124
Default

You cant drill your own KO holes in the red boxes.
Use stranded if you have a problem with breaking terminals.(cheap plastic)
Duct smokes have little room for wiring. (Flex out of a JB)
Once saw a guy use 4" gutters out of the top of tubs. Couldn't reach his hand inside to pull the wire. (use 6" gutters)
ElectricMetalTuba is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Fire alarm guy hancholo General Electrical Discussion 10 06-20-2016 05:56 AM
fire alarm bell connected to receptacle cct PlugsAndLights General Electrical Discussion 4 06-03-2016 09:57 PM
New To Fire Alarm LanceBass General Electrical Discussion 3 04-14-2016 06:20 AM
Fire Alarm How To Book LanceBass General Electrical Discussion 19 03-26-2016 04:40 PM
Mircom Fire Alarm darren79 Canadian Electrical Code Forum 8 02-24-2016 11:33 PM


All times are GMT -4. The time now is 02:37 PM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.1
vBulletin Security provided by vBSecurity v2.2.2 (Pro) - vBulletin Mods & Addons Copyright © 2017 DragonByte Technologies Ltd.
User Alert System provided by Advanced User Tagging (Pro) - vBulletin Mods & Addons Copyright © 2017 DragonByte Technologies Ltd.
Our Pro Sites Network
ContractorTalk.com | DrywallTalk.com | HVACSite.com | PaintTalk.com | PlumbingZone.com | RoofingTalk.com