Old 01-27-2009, 05:48 PM   #1
Default GFCI alarms?
Never have been asked to solve anything like this, not my line of work. Your help would be much appreciated.
A commecial building with 4 heat tape/wire in 4 roof drains wired to 4 30amp GFCI's. The gfi's have tripped twice in 2 years causing damage to drain system. I need an alarm to sound when any 1 of the 4 breakers trip. A local supplier says to use a shunt and alarm in the panel to a gfi meant for the heat tape. Wouldent the gfi still trip before the shunt breaker does meaning no alarm would sound? He also said there is no GFI shunt, yet I see some stuff online from squareD using the words "ground fault alarm". sounds like what I need but the panel is seimmens. Is this a monitoring system solution or a breaker solution? I am not familiar with either.
thanks, Charlie
charlie s. is offline   Reply With Quote
Old 01-27-2009, 07:17 PM   #2
mattsilkwood's Avatar
i would use relays off the load side of the gfi with your alarm hot through the nc contacts.
so in other word when your gfi trips your relay drops out and makes the alarm circuit. cheap and simple
Old 01-27-2009, 07:25 PM   #3
Ditto. Or send it to the alarm/security panel, Now you have remote monitoring for the weekends.
Old 01-27-2009, 09:35 PM   #4
You can order most molded case circuit breakers with a "bell alarm contact". Takes up an extra pole space, and has a set of contacts that make when the breaker trips. If Square D add "-2100" to the end of the breaker part number.
Old 01-28-2009, 09:56 AM   #5
thats pretty cool marc, i dont think ive ever seen anything like that
Old 01-28-2009, 06:33 PM   #6
I was an electrician at a gold plating plant for a number of years, and we used the GFCI's with the alarm contact for the bath heaters quite extensively. The contact was just switching a PLC input to put a warning on the HMI. It wouldn't shut the line down unless the bath temp started to drop below spec. The warning gave an electrician a chance to change out the heater while the line was still running.
Old 01-29-2009, 10:15 AM   #7
Wyome
Damn, this counts as my something new today.
Wireless Fire Alarms? jfpenkala General Electrical Discussion 0 01-05-2009 03:14 PM
smoke alarms residential the_full_monty General Electrical Discussion 25 01-04-2009 04:54 PM
testing domestic smoke alarms coop1 UK Electrical Forum 4 09-21-2008 06:10 PM
does this need a GFCI? gcleary47 NEC Code Forum 3 06-19-2008 07:32 AM
You do fire alarms? MDShunk Structured Wiring 16 10-16-2007 08:50 PM