We are trying to size a generator for a warehouse, and these are the loads:
Three 7.5 Ton a/c units, 480V. each unit has two compressors rated
5.2 RLA, 44 LRA.
Two 277V. 20A circuits with 10 fluorescent lights (T-8, 6 lamps)
The owner wants to have a automatic transfer switch, I know we need a generator big enough to handle the start of the compressor, but is there a way we could delay the start of the second and third one?
I will appreciate any suggestions, thanks.
electron is offline   Reply With Quote
Old 05-01-2012, 10:55 PM   #2
kbsparky's Avatar
A load-shedding transfer switch would be one method.
Barring that, I'd use some time-delay relays on the control wiring with different values set on each HVAC unit, so they won't all try to start at the same time.
-KB
The Following User Says Thank You to kbsparky For This Useful Post:
electron (05-03-2012)
Old 05-02-2012, 03:43 AM   #3
animal lover /rat bastard
wildleg's Avatar
I agree with kb. phase loss monitors with adjustable restart times
Old 05-02-2012, 08:04 AM   #4
mbednarik's Avatar
check with the HVAC co. I ran into some geothermal heat pumps a while back that had a random restart time so that two units would try to start at the same time.
The Following User Says Thank You to mbednarik For This Useful Post:
Old 05-03-2012, 10:59 PM   #5
Thank you for all the replies, I just went back to the warehouse today and took some measurements and these is what I got:
Unit #1,
Starting Amps= 12A, after 6sec. will drop to 4A,
after 2 or 3 min. I guess the second comp. kicked in and it went up to 17A,
after 6 sec, it went down to 13.8A and it was stable at that until the
thermostat will cut off, then it just repeats the cycle. It did the same in all
phases with 2 or 3 amps of difference. I was king of surprised since the
data plate shows 44LRA, but I am not sure if I'm missing something.
Help sizing 3-phase generator erics37 General Electrical Discussion 27 03-17-2012 01:11 PM
Sizing a generator ahrambakr General Electrical Discussion 13 06-15-2011 01:08 PM
stand alone generator dogleg General Electrical Discussion 1 11-22-2010 11:00 AM
Generator sizing garfield General Electrical Discussion 4 07-16-2010 09:24 AM
Generator Sizing Mountain Electrician General Electrical Discussion 23 06-03-2008 06:08 AM