Old 05-03-2012, 11:47 PM   #1
Default sizing transformer for loadbanking
I have a 2megawatt 480 load bank used for generator testing. I need to size a transformer so I can test 4160 volt. The normal way would use a 2500 kva transformer. I plan to make it portable. I need to get the weight down as much as posiblle. I have tested using a 2500 kva and there is no temp rise with the transformer. The duty cycle will be no more than 5 hours. my thought would be down size and lose weight to make it more portable. What are your thoughts. Thanks
Generator51 is offline   Reply With Quote
Old 05-04-2012, 02:56 AM   #2
I would sub it out,rather than getting into all that cabling and terminations
Old 05-04-2012, 10:36 PM   #3
I am the sub the is doing this work. The 4160 side does not have that much wiring. I just don't think you need a full size transformer for just a short duty cycle Thanks
Old 05-05-2012, 10:14 AM   #4
BBQ
BBQ's Avatar
I think if you contact a major transformer manufacturer they could help you with this.
Power companies regular 'overload' transformers knowing that the length of the overload will not overheat the transformer.
You could also ask about using forced cooling with fans or maybe even water.
BBQ is online now   Reply With Quote
brian john (05-05-2012)
Old 05-05-2012, 11:07 AM   #5
Bob, all that is part of doing load test.
Brian John
Leesburg, VA
Old 05-05-2012, 11:08 AM   #6
Are you using a dry type or oiled filled?
Brian John
Leesburg, VA
Old 05-05-2012, 04:40 PM   #7
I would like to use a oil filled. I will not use to much, so it will be easer to store. I am open to anything right now. Some of the thoughts I have are the busing in the transformer. Will they carry the short large load. I know transformers can overload. I haven't a lot of experance over loading transformers. Fan cooling is more of a long term fix. I would like to find a used transformer. Cost savings would be nice for the small amount of time I will use it. Thats why I'm here, to see if someone has some backround in this area.
Old 05-05-2012, 05:44 PM   #8
First what are your typical load steps and duration at each load. In a 5 hour load test you are at 100% what 1-2 hours?
http://www.usbr.gov/power/data/fist/fist1_5/vol1-5.pdf
Brian John
Leesburg, VA
Old 05-05-2012, 10:46 PM   #9
Load Test starts 25% one hour,50% one hour. 75% one hour, 100% two hours. at 100% it pulls a little over 2400 amps. 480 volts
Old 05-06-2012, 12:48 AM   #10
I'm thinking you're going to have some transportation issues to tend with if you use an oil-filled transformer. Placarding, containment, hazmat endorsement for driver, etc.
Big John (05-06-2012)
Old 05-06-2012, 11:36 AM   #11
1,000,000th Poster
Big John's Avatar
That's my thinking. I would suggest a dry-type, but you've gotta have a reasonably conditioned place to store it, or else get an encapsulated style. You can't leave the thing sitting in a yard somewhere.
-John
Big John is online now   Reply With Quote
Old 05-06-2012, 12:15 PM   #12
-John
I have seen it done time and again. THOUGH NOT RECOMMENDED
Maybe two dry types on two trailers parallel them, easier to transport.
Brian John
Leesburg, VA
Old 05-06-2012, 12:54 PM   #13
I ideal way is two trailers. I'am tring to keep travel time down. I live in central California. I travel south as far as the Mexican border, north to the Calif border. You can see road time needs to be kept down. What I need to Know is how small a Transformer I can use and make it work. Like will a 1200 Kva work without damage to it. Due to duty cycle
Transformer Sizing Help newspark80 General Electrical Discussion 13 12-17-2011 10:46 PM
Transformer sizing Paul85 General Electrical Discussion 1 10-04-2011 06:40 PM
POCO Transformer Sizing Cletis General Electrical Discussion 8 09-14-2011 07:01 PM
GEC to CEE Sizing eutecticalloy NEC Code Forum 16 02-08-2011 10:13 PM
transformer sizing ???? Vr_ecobox Services and Service Equipment 1 12-07-2007 07:49 PM