Old 05-09-2012, 08:30 PM   #1
Default Split Delta Ground Detection Problem
I have a 480 ungrounded system with split delta ground detection. The primaries are connected to the 480 bus in a grounded wye. The secondaries are connected in a delta with a 64 (ground detection relay ) and a dampening resistor between the 2 phases that form the apex of the delta. It looks to have 2 high resistance grounds on 2 phases and the 3rd phase is ungrounded. We connect the thumper and there is no current flow during the pulses. The 64 relay does not pick up there is anout .2 amps of current through the resistor. No breakers have triped and the line to line voltage is 480. The line to ground voltages are like 150 220 and 390 from memory .
Any ideas ?
THANKS
Electrician licensing without continuing education is just another form of TAXATION
Old 05-09-2012, 08:37 PM   #2
1,000,000th Poster
Big John's Avatar
Are your voltages normally pretty constant? I wouldn't expect voltages on faulted phases to be that high.
Depending on how well sized the resistor is on your broken delta, you can have a good bit of circulating current flowing through it, and this will change if system capacitance changes. Do you know for sure that's a new problem?
-John
Old 05-09-2012, 09:49 PM   #3
We have faught this problem off and on for more than a year. I know that the transformers have been replaced twice . What determines the setting of the resistor. I believe that we had 3 volts and .2 amps today. I will get the correct figures tomarow.
LC
Old 05-10-2012, 05:35 PM   #4
The voltage readings are as follows
A-B 484
B-C 489
C-A 482
Ground Detection Fuses Out
A-G 159
B-G 336
C-G 372
Ground Detection Fuses In
A-G 260
B-G 253
C-G 333
The line to line voltages are the same with the ground detection fuses in or out.
There are 120 volt indicator lamps across the secondary of each of the transformers and their voltages are as follows
A- 32
B- 88
C- 102
That is all I can tell you
Old 05-10-2012, 06:02 PM   #5
1,000,000th Poster
Big John's Avatar
Can you guys put a monitor on this to see how it changes with load? I think you have a single soft ground on A and the rest of the voltages are just floating to follow it.
How big is this system, what kind of loads are on it?
-John
Old 05-10-2012, 06:12 PM   #6
Feeder to a building probably 500' long to a MCC then HVAC motors and duct heaters
Old 05-10-2012, 06:26 PM   #7
1,000,000th Poster
Big John's Avatar
Is it impossible to isolate downstream loads by opening breakers and seeing if the voltage stabilizes? It's really strange that you're getting no current flow at all with your thumper.... Any change in phase voltage when it's connected?
Also: Why have you had to replace the transformer twice?
-John
Upgrade No ground delta?? Cletis NEC Code Forum 14 03-19-2012 05:42 PM
Ground Detection Lamps Lone Crapshooter General Electrical Discussion 4 02-28-2011 09:38 PM
Ground on 600 volt delta sparky105 Services and Service Equipment 6 01-12-2011 08:29 PM
Help! Corner ground delta (CGD) system. teal854t General Electrical Discussion 11 10-14-2010 02:06 PM
Ground Fault Detection Scheme DipsyDoodleDandy Commercial Electrical Forum 19 01-03-2010 08:02 PM