Electrician Talk - Professional Electrical Contractors Forum
CLICK HERE AND JOIN OUR COMMUNITY TODAY...IT'S FREE!
Go Back   Electrician Talk - Professional Electrical Contractors Forum > Electrical Trade Topics > Commercial Electrical Forum

Reply
 
Thread Tools Search this Thread Display Modes
Old 05-07-2012, 11:17 AM   #1
Junior Member
 
Join Date: Apr 2012
Location: San Diego, CA
Posts: 8
Default VFD/Motor Overcurrent Protection???

Looking to install a 50HP VFD for a Chilled Water Pump. I'm a little old school and always protect my motors at 175% assuming I'm using a thermally protected breaker or time delay fuses. What I need to know is, can I use 125% due to the fact it will not be set up for full voltage start?

50HP 3-phase 65amps @460v
65amps @ 125% = 81.25amps or 90amp breaker/fuse #4wire.

or

65amps @ 175% = 113.75amps or 125amp breaker/fuse

your thoughts?

Dube2 is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectricianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!
Old 05-07-2012, 12:03 PM   #2
Junior Member
 
Join Date: Apr 2012
Location: San Diego, CA
Posts: 8
Default

GOT IT! NEC 430.126 and referance to 430.32. 125%

Dube2 is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Overcurrent protection - motor circuit Mike in Canada Canadian Electrical Code Forum 7 03-26-2012 04:47 PM
Derating and Overcurrent Protection Turtle3000 NEC Code Forum 5 03-03-2012 05:42 PM
Overcurrent Protection FireInTheWire NEC Code Forum 3 01-21-2012 11:20 AM
Overcurrent protection newspark80 Residential Electrical Forum 4 08-12-2011 01:35 PM
overcurrent protection chart? SILENT BOB General Electrical Discussion 21 08-26-2008 08:56 PM

Top of Page | View New Posts

All times are GMT -4. The time now is 02:42 PM.


Electrician Talk © 2006 - 2010 The Building Network

Search Engine Optimization by vBSEO 3.6.0 RC 2