10-04-2009, 09:16 PM
#41
Unlimited Lic.Electrician
Originally Posted by rlc3854
Check out the other three cables in the upper left side. They look gray
Yea, I noticed that.
10-04-2009, 09:20 PM
#42
If I had to replace a X-fmer I think I would take the top off and use a cherry picker and unbolt the x-fmer from the housing and lift it strait out of the top. You wouldn't have mess with knocking out the holes in the new housing or mess withe the wires execpt reterminating them.
10-04-2009, 09:28 PM
#43
Senior Moment
Oh, and by the way William that sure is some pretty work-beautiful.
10-04-2009, 09:29 PM
#44
Thank you.
10-05-2009, 02:47 AM
#45
transformer wiring
William / 480,
Thanks for the diagram:
Dis do it?
So this idea is to delta connect the wye 480 to the transformer by leaving off the neutral. I understand that most transformers use a delta primary. But now I need to think hard about any problems this might cause in the overall system.
Are there many loads that use 480 wye, so that making up the whole system as 480 delta would not work? Saving the cost of the neutral might be worthwhile system-wide.
The delta connected transformer primary could potentially have a phase current imbalance that would have otherwise been carried by the primary neutral connection (if wye).
Also I thought harmonic currents would cause more heating in delta than in wye.
Time to put on my thinking cap.
Thanks for the education.
EJPHI
10-05-2009, 04:58 PM
#46
I had lights that were 277v so in my case I did need the neutral,but if there was no neutral load you could do without the neutral I suppose.
10-05-2009, 04:59 PM
#47
EJPHI are a engineer?
10-05-2009, 05:31 PM
#48
EJPHI are an inguneer. The electronical kind not the choo-choo kind.
EJPHI
10-05-2009, 06:11 PM
#49
I would prefer to have a house designed around the things I do every day, like cook, do laundry, sit at the computer and post on ET...........
And carry in groceries
I put my laundry room next to the bedroom so I don't have to drag the laundry across the house and back. It seems to me that a well designed house would always have the laundry close to where the clothes are but they still always put them across the house by the kitchen/garage.
Crap....I forgot what the thread was about
10-05-2009, 06:26 PM
#50
B4T Scotchkote installer
EJPHI
I have no idea what he is saying......
10-05-2009, 06:32 PM
#51
Not Peter D
Those who operate trains are also referred to as engineers.
10-05-2009, 07:20 PM
#52
You are not alone.
Sometimes I don't either
10-06-2009, 12:11 AM
#53
I like roughing em in the slab. What I do is stub up beside the xmfr into a JB bolted to the side of the xmfr. Makes it much easier to replace.. and pull the wire too.
10-06-2009, 12:36 AM
#54
Going back a few posts, there are basically two reasons I can think of as to why most 480 volt services are wye;
1) 277 is available for lighting. This can be the majority of the load in a lot of buildings.
2) The maximum voltage to ground is 277. If the service was 480 grounded B, two legs would be 480 to ground. If it was a 4 wire delta, two legs would be 240 to ground, and the other one would be 416 to ground. Obviously, a wye is slightly safer.
There are a few reasons why most transformers are delta/wye.
1) A closed delta connection tends to balance voltage. A wye/wye will pass any imbalance through.
2) Coil and core heating is a bit more evenly distributed when a current imbalance exists on the secondary.
3) A current imbalance in the secondary results in less of an imbalance in the primary.
4) A delta/wye tends to diminish the effects of harmonics passed back to the primary. A wye/wye tends to magnify it.
I'm sure there are others, these are just what comes to mind right now.
Rob
10-06-2009, 04:44 PM
#55
The POCO around here will not cut on a transformer that doesn't have a grounded conductor in the conduit.
10-06-2009, 06:52 PM
#56
They don't provide Delta services?
John from Baltimore
"One day at a Time"
10-06-2009, 09:36 PM
#57
No.........
10-08-2009, 02:00 AM
#58
Rob
Micromind;
All i can say is DOOH! I forgot about the lighting load.
Pardon the pun, but your comments above were quite illuminating!
I will give this some more pondering.
EJPHI
10-17-2009, 08:47 AM
#59
Professional Nit Picker
Let me play devils advocate here.....
The transformer in the picture does not have a factory "open bottom", but rather a slotted " vented" bottom.
In the 2008 NEC Section 300.12 Mechanicl Continuity -
"Raceways and cable sheaths shall be mechanically continuous."
You can not just cut a hole and stub a conduit up into it any more.
The one in the pictures is installed just that way. Those pvc Bell ends are not connectors. SO that means that there is no Mechanical Continuity.
To acheive mechanical Continuity you must use an approved conector that is connected directly to the transformer.
Comments ?????