Disconnecting Neutral - Electrician Talk - Professional Electrical Contractors Forum
Old 06-11-2012, 05:28 PM   #1
Rewards Points: 524
Default Disconnecting Neutral
Is there a code that prohibits you from disconnecting the neutral in a service disconnect for an a/c unit? The line is also disconnected. Only thing I can find is Rule 4-026.
120v unit with 2p breaker in disconnect.
CanadianSparky is offline   Reply With Quote
Old 06-11-2012, 07:02 PM   #2
Rewards Points: 268
So you're talking the grounded and ungrounded conductors, each on one pole of the disconnect....
The best that I can think of is:
14-016
Devices required by this section shall not be connected in any grounded conductors EXCEPT where
(a) the devices simultaneously or previously disconnect all ungrounded conductors;
So sounds like you could if wanted?
The only problem I can think of is someone replacing the AC might think it's a 240v supply and hook up a 240v unit?
sprdave is offline   Reply With Quote
Old 06-11-2012, 07:13 PM   #3
Rewards Points: 524
14-016
Correct and I agree with your last statement. But also the next installer should be reading the specs on the previous units/know the voltage and amperage that\s being supplied to the unit. But then again we know how that always goes.
Old 06-11-2012, 08:14 PM   #4
So you feed the D/C with a 3-wire on a 2-pole breaker? Or your just using a 2-pole D/C fed by 2 wires?
Technically you have an identified conductor, since you have 120v. Nothing I saw in the CEC about them either though.
I think you fall in to the exception of that rule, I just don't see any reason to do it. If you put both on, you risk that someone thinks its 240/208. The next guy should know what he is doing, but Ive seen electricians make that mistake, let alone home owners /wanna be electricians. You could just as easily splice the identified conductor and leave 1 pole of the D/C open.
Cujo is offline   Reply With Quote
Old 06-11-2012, 09:59 PM   #5
Rewards Points: 5,198
No, or, at least, there shouldn't be.
Lets talk Disconnecting Means. thegoldenboy NEC Code Forum 16 04-05-2012 07:50 PM
Disconnecting 2 PV Source Circuits w/1 Disconnect NJWVUGrad Alternative Energy Forum 6 12-20-2011 07:13 AM
Cost of disconnecting old circuit SPINA ELECTRIC Business, Marketing, and Sales 9 04-01-2010 09:31 PM
means of disconnecting stillirnin NEC Code Forum 2 10-07-2008 04:05 PM
Walk-in Freezer Disconnecting Means Kwato18 NEC Code Forum 10 06-29-2008 01:47 PM