Old 04-26-2012, 02:05 PM   #1
Aegis's Avatar
Default Romex Above T-bar? (CEC)
We're in a commercial building and they're building walls with wood studs. They're also putting a drop ceiling (t-bar) in. Can you run non metallic sheathed cable above a drop ceiling?
Aegis is offline   Reply With Quote
Old 04-26-2012, 02:11 PM   #2
If you are asking about code No see 334.12
EC2253 is offline   Reply With Quote
Old 04-26-2012, 02:13 PM   #3
Aegis's Avatar
I am asking about code yes CEC
Old 04-26-2012, 04:42 PM   #4
The wire method used is going to depend on the materil used to build the outside walls of the building. Combustible or non combistible. Then choose your wire. Also dont forget the ft4 requirements if the dropped ceiling becomes a plenum.
arni19 is offline   Reply With Quote
Old 04-26-2012, 04:52 PM   #5
Aegis's Avatar
The building is non-combustible. Inside is a small area that's built with wood studs. I know I can use Romex in the studs and BX everywhere else. If the return air is all in closed ducts above the t-bar would It then be ok?
Old 04-26-2012, 05:01 PM   #6
Yeah , you should be fine.
Old 04-26-2012, 07:04 PM   #7
Electron Pathway Engineer
Yes, most A&W's are done that way. Just finishing one up near Ottawa.
Old 04-26-2012, 07:06 PM   #8
Aegis's Avatar
Thanks guys. Is this a mix of CEC and building code?
Old 04-26-2012, 07:08 PM   #9
it's above 3 feet and doesn't need mechanical protection. If it's wood construction NMD90 is permissible as per electrical code.
Old 04-26-2012, 08:39 PM   #10
Above the drop ceiling is okay if it isn't a return air. 12-010, 2-126 and Appendix B 2-126. You need FT4 rating in a return air and NMD is FT1 or FT2.
xlink is offline   Reply With Quote
Old 04-26-2012, 08:41 PM   #11
B4T
ET Road Warrior
B4T's Avatar
Good to see you guys are not following the craziness we have down here about NM above suspended ceilings in commercial buildings..
But the real insanity test is if your code allows NM in a wet location..
Example would be NM sleeved in conduit on the outside of a house to feed an AC unit..
The Associated Press wants to stop using the term "Illegal Aliens".. they say it is demeaning.. .. instead they want us to use Undocumented Democrats... Jay Leno..
Old 04-26-2012, 10:21 PM   #12
Our code allows only NMWU not NMD to be used outside.Inside a conduit exposed to the weather is considered a wet location.Seal tite or teck from the w.p. disconnect is typically used in these situations.
crosport is offline   Reply With Quote
Old 04-28-2012, 05:15 PM   #13
magneticpersona's Avatar
In BC, the fire code requires a FT4 rating for any wiring in plenum (drop ceilings) in commercial installations. This means no loomex, and your closest FT4 equivalent is Ac90 for normal voltages.
magneticpersona is online now   Reply With Quote
Old 05-12-2012, 11:40 AM   #14
Not all t-bar ceilings are considered plenums. If the ceiling is used to transport air rather than using ducts then you have to go with ft4 rated cables. I've only ran into a few in my area that were actually considered plenums. As long as it's wood framed you're usually okay to go with NMD.
Nigelforsythe is offline   Reply With Quote
Old 05-12-2012, 02:28 PM   #15
while i agree not all drop ceilings are considered plenums, the inspectors still don't pass it in my area. Their logic is that if it could become a return air plenum that it must be wired with FT4 wires. This is especially true of any commercial installation i have ever done. When it comes to residential, who knows. All that mathers is if the inspector likes it or not, and here they don't
For perfect electrical work at a great price!
www.absolutelyperfectelectrical.com
Old 05-12-2012, 02:57 PM   #16
here is proof that this is not allowed:
rule 2-126(b)(ii) appendix B
FT4 to be used in spaces between a floor and a ceiling or ceiling and a roof,that may be used in as a plenum (that means current or possible future installation) in buildings of combustible or non-combustible construction. Its against building code too.
Old 05-12-2012, 09:00 PM   #17
That's an unreasonable interpretation of that statement.
I would have thought a reasonable inspector would first look at the space to determine if it "may be used" as a plenum. If there are no return air ducts connected to the space, a reasonable person would conclude that it certainly can't used as a plenum, so it doesn't fall into the scope of a space that "may be used" as a plenum.
In any event, although Appendix B is a good guide, it isn't code. See the note under the heading.
Your inspectors would have a better argument if the National Building Code said that spaces that aren't plenums are subject to the same rules as plenums, but until I see that, if it isn't a plenum, it simply isn't a plenum.
Thankfully, such obscure interpretations are restricted to the island.
Old 05-12-2012, 11:41 PM   #18
edit: two of the same thread??
NMD in Drop Ceiling
mattwright999 is offline   Reply With Quote
2/3 romex Magnettica General Electrical Discussion 48 06-04-2012 11:11 AM
No romex 220/221 Services and Service Equipment 1 08-29-2011 08:53 PM
bx or romex judadamo NEC Code Forum 4 05-31-2011 09:13 PM
Romex in 1/2 emt AMPED General Electrical Discussion 5 05-12-2011 01:39 PM
Mc Or Romex Or Bx Nitro9119 General Electrical Discussion 3 05-19-2008 08:48 PM