I am working a place with severe undervoltage due to heavy loads.
As low as 85 volts on the 120 legs of 240v edison system.
What I want to do is have an interconnected generator, like 15kw size, to bring up the voltage, but still use poco juice.
Can I do this affordabely? Or am I going to have to do some weird dc setup with inverters? Or just put in a temp panel fed from a stand alone generator, and move some loads over there...
miller_elex is offline   Reply With Quote
Old 10-09-2016, 11:18 AM   #2
animal lover /rat bastard
wildleg's Avatar
Rewards Points: 458
has anyone discussed poco based solutions with poco ?
Old 10-09-2016, 12:00 PM   #3
Click Here
Rewards Points: 1,410
I know I am dabbling here in smart people stuff in which I don't belong, but if a measly 15Kw or less is enough to correct the undervoltage, then there must be a serious problem elsewhere.
Majewski likes this.
Old 10-09-2016, 02:02 PM   #4
Rewards Points: 340
Obviously poco solution would be best but unless you split up the load you will need parallelling equipment. I don't think those units are cheap though the only one I saw a price for was for a 200ka system so...
Edit -not to mention the danger to lineman of having back fed generator systems. I doubt they would approve it on such a small scale
Big John likes this.
Anathera is online now   Reply With Quote
Old 10-09-2016, 02:31 PM   #5
Donuts > Fried Eggs
Big John's Avatar
Rewards Points: 286
In theory your generator would only have to be sized to pick up the kVA that you are sagging. My concern is that when grid parralleled you would actually be trying to carry everything on that local grid that was below your nominal voltage; you might need a massive generator to do that.
Add in the fact that you'd need paralleling gear, utility tie protection, an intertie agreement, and the customer would be bearing the fuel costs indefinitely, I really don't think this is the right solution.
If you can prove the undervoltage is occurring at the service the utility may have a duty to upgrade to keep you within 5% of nominal. I'd start there.
micromind and splatz like this.
Big John is online now   Reply With Quote
splatz (10-09-2016)
Old 10-09-2016, 03:33 PM   #6
Semper Fidelis
Suncoast Power's Avatar
Rewards Points: 4,574
Question:
Are your larger loads intermittent or continuous?
Old 10-09-2016, 03:36 PM   #7
Rewards Points: 13,684
This matter is for the Poco to resolve. Period.
Too many cooks spoil the waveform.
Suncoast Power (10-09-2016)
Old 10-09-2016, 08:42 PM   #8
Rewards Points: 798
Where did you mesure the voltage at ??? that will make the differnce there.
I would not bother do that because the cost as Big John mention it clear...
I will get on the POCO first and let them know about undervoltage sistuation after only you verify the customer side conductors and connection is good .,,
if customer side is good then ping the POCO and they will have to keep the voltage to normal level on full load.
Old 10-09-2016, 10:13 PM   #9
That's a fact, Jack.
frenchelectrican likes this.
100 KW Generator Modification. ROCKDOG General Electrical Discussion 15 08-08-2016 02:31 AM
100 KW Portable Generator Modification ROCKDOG Services and Service Equipment 7 08-06-2016 09:39 PM
Multiple ATS configuration with Generator katwalatapan Commercial Electrical Forum 0 06-02-2016 01:05 PM
Max height for Generator? nyerinfl General Electrical Discussion 8 03-09-2016 04:51 PM
Neutral required to be ran to generator? lynes.nathan Canadian Electrical Code Forum 7 03-01-2016 09:10 PM