PV conduit inside exterior wall permitted? - Electrician Talk - Professional Electrical Contractors Forum
Like Tree9Likes
  • 1 Post By macmikeman
  • 1 Post By papaotis
  • 2 Post By MechanicalDVR
  • 2 Post By Suncoast Power
  • 1 Post By backstay
  • 2 Post By macmikeman
Old 11-04-2016, 01:42 PM   #1
Rewards Points: 205
Default PV conduit inside exterior wall permitted?
Hello,
I'm working on a plan to install 4kW, 1-phase, 240VAC, grid-tied, micro-inverter based, Photo-Voltaic System no a rooftop in a multi-unit residential building. I wanted to inquire if it is an acceptable practice to run the AC cables from the rooftop junction box to the PV AC Disconnect on the buiding's exterior wall, in EMT conduit installed inside the building's exterior wall. Exterior wall cladding work is also planned around the same time, so I wanted to inquire if it is acceptable to run the EMT conduit inside of the exterior wall.
This work is conducted on an existing building, so going through the attic and ceiling space of the building is not an option. Another alternative could be installing the EMT conduit from the rooftop junction box on the surface of the exterior wall. I'd appreciate your comments/suggestions on the best practice to install the EMT conduit from the rooftop junction box to the PV AC disconnect on the exterior wall. Also, is rigid EMT conduit preferable or flexible, galvanized steel conduit?
Thank you.
katwalatapan is offline   Reply With Quote
Old 11-04-2016, 01:55 PM   #2
Rewards Points: 2,196
Originally Posted by katwalatapan View Post
Hello,
Thank you.
Majewski likes this.
Old 11-04-2016, 10:15 PM   #3
corn-fused
papaotis's Avatar
Rewards Points: 208
ditto
Old 11-04-2016, 10:20 PM   #4
Deplorable-Electrician
Rewards Points: 8,950
Galvanized flex (Greenfield) isn't a material choice I'd select for this, I'd stay with PVC sch 40 conduit myself.
20 Jan 2017 Truly a great day in American history!
End of an ERROR!
Old 11-04-2016, 10:21 PM   #5
Semper Fidelis
Suncoast Power's Avatar
Rewards Points: 3,456
Inside of the exterior.
Is that the interior?
glen1971 and papaotis like this.
or just enjoy the show.
Old 11-04-2016, 10:59 PM   #6
NRA Member
backstay's Avatar
Rewards Points: 516
For some reason I thought PVC wasn't allowed from the panels down inside the building. I looked and couldn't find it. Micro inverters change things.
backstay is online now   Reply With Quote
Old 11-05-2016, 10:39 AM   #7
wcord's Avatar
Rewards Points: 602
If you are asking if EMT conduit can be buried in a wall (insulated or not) the answer is yes.
It is only PVC conduit, that has a restriction of not being buried in insulation.
As to recommendation of method, unless you want/need the ability to modify the conductors in the future, I would consider Teck
Be careful what you wish for, you just may get it.
Old 11-05-2016, 11:32 AM   #8
Rewards Points: 4,356
Correct. PVC conduit cannot be surrounded by thermal insulation. Don't ask me for the rule number. If it's strapped to a stud then, technically, it's not surrounded by insulation but I might expect a fail anyway.
Old 11-05-2016, 01:09 PM   #9
This is the alternative power forum section not the Canadian section right? Ok, good. Pvc can be buried in insulation all day and night. DC current conductors coming from solar panels must be in metal conduit once inside the interior of a building. I have no idea if the inside core of an exterior block wall is considered interior or exterior. This is my coup to restore the sovereignty of this forum!
Cl906um (11-19-2016)
Old 11-05-2016, 04:05 PM   #10
wcord's Avatar
Rewards Points: 602
the OP is from Canada, so our superior code rules apply
Old 11-05-2016, 04:51 PM   #11
macmikeman, welcome to the New World Order!. It only gets better and better
Old 12-05-2016, 01:09 PM   #12
aDudeInPhx's Avatar
Rewards Points: 262
I have done a lot of outside piping of interior walls, so my experience is completely opposite from what would not not help you here.
aDudeInPhx is offline   Reply With Quote
Paging the Conduit Whisperer A Little Short Commercial Electrical Forum 21 07-13-2016 02:11 PM
Conduit fill for water feature fountain Sprink General Electrical Discussion 3 04-27-2016 08:03 PM