Old 03-29-2010, 07:39 AM   #1
Default 2008 NEC and art. 702.5 capacity & rating
Good day, could anyone indicate what is the proper way to calculate the proper size standby generator? Also how you calculate the deals with the maximun available short current at its terminals.
How to deal with motor loads on A/C units with high LRA?
thanks
holtjgh1128 is offline   Reply With Quote
Old 03-29-2010, 10:34 AM   #2
Ax grinder
raider1's Avatar
Welcome to the forum.
I would suggest that you ask each of those questions in a separate thread as they each could require quite a bit of explanation.
As for how to size a standby generator, what type of transfer switch are you going to use, automatic or manual? The answer makes a great deal of difference.
Chris
Old 03-29-2010, 02:42 PM   #3
Default automatic standby with auto transfer switch, Onan, Kohler
thanks for the response. I install all sizes and wanted to see how others view the new 2008 section of 702.5
thanks
Old 03-29-2010, 04:57 PM   #4
Ax grinder
raider1's Avatar
I view it very simply, if you install an automatic transfer switch then you have 2 options for sizing the generator.
1. Size the generator for the full load to be transferred by the transfer switch.
2. Provide a load management system that sheds unnecessary loads and size the generator for the managed load.
Also 702.5(A) requires that optional standby system equipment be suitable for the maximum available short circuit current at its terminals.
Chris
transformer overloading capacity mpower2010 General Electrical Discussion 5 02-03-2010 08:48 AM
generator rating charlie Bob General Electrical Discussion 10 12-23-2009 12:51 AM
De-Rating simplified? Electrician343 General Electrical Discussion 13 05-02-2009 11:15 AM
temperature rating EMC General Electrical Discussion 25 04-23-2009 06:59 PM
Breaker capacity dora General Electrical Discussion 8 03-15-2007 10:02 PM