Old 08-13-2008, 04:46 PM   #1
Default 2008 residential code changes
I'm wiring my first new house since last summer. Are there any new codes I should be aware of other than these?
AFCI circuits
Tamper-proof receptacles
Ufer-ground
Xknob&Tube is offline   Reply With Quote
Old 08-13-2008, 05:27 PM   #2
Ax grinder
raider1's Avatar
There are a lot of changes in the 2008 NEC that relate to home wiring. Here are a few that you didn't list:
1. 210.4(B) a common disconnecting means for all multiwire branch circuits.
2. 210.8(A)(2) & (A)(5) Exceptions 1 and 2 were delected, this means ALL 120 volt 15 and 20 amp receptacles installed in garages and unfinished basements must be GFCI protected.
3. 210.52(E)(3) requires balconies, decks and porches that are accessible from inside must have at least one receptacle installed.
4. 250.94 the intersystem bonding means now must have provisions for connection of at least three bonding conductors.
5. 334.80 has expanded the romex bundling to include bundling within thermal insulation
6. 338.10(B)(4)(a) requires that SER cable installed within a building for feeders and branch circuits must be sized from the 60 degree column in accordance with 334.80.
7. 310.15(B)(6) the ampacity chart for service and main power feeders has been clarified to show that it only applys to a single main power feeder that carrys the entire load of the dwelling.
These are just some of the changes that I could think of off the top of my head but there are many more.
Chris
Old 08-13-2008, 05:31 PM   #3
kawaikfx400's Avatar
weather resistant and tamper resistant plugs in outside plugs
anything that is not an appliance or GFI protected has to be arc fault.
tamper all over the house.
Any others i can think of, i'll let ya know. We only do residential for the most part.
kawaikfx400 is offline   Reply With Quote
Old 08-13-2008, 06:58 PM   #4
Multi-wire branch circuits cannot be used with arc-fault breakers anyway.
If I have a single receptacle for a freezer in the garage must it be GFI protected?
A single receptacle for a sump-pump in the basement?
Chris, I don't really understand 250-94. How does that affect a residential service (in english)?
Old 08-13-2008, 07:21 PM   #5
They can if you buy a 2pole AFCI breaker.
Yes & Yes, but dont worry the freezer or the sump pump will still work.
Stickboy1375 is offline   Reply With Quote
Old 08-13-2008, 10:12 PM   #6
http://www.dora.state.co.us/electrical/
Welcome to the club!
Time to buy the book!!
leland is online now   Reply With Quote
Old 08-14-2008, 10:36 AM   #7
Ax grinder
raider1's Avatar
As Stickboy has pointed out there are 2 pole AFCI breakers.
Yes, a single receptacle for a freezer must now be GFCI protected, as well as a single receptalce in a unfinished basement for a sump pump.
As for 250.94. The 05 NEC required a way to bond telephone, CATV, and other systems to be installed at the electrical service. You could use a metal service conduit, or an exposed section of the grounding electrode conductor. But the 2008 NEC now requires that you install a ground bar with at least 3 terminals to either the meter enclosure, or on the wall next to the service disconnecting means and bonded to the service disconnecting means with a minimum of a #6 bonding wire.
Hope this helps.
Chris
Old 08-14-2008, 10:48 AM   #8
Do you still need the intersystem bond terminals if the GEC is accessible?
You also need to install at least one communications outlet, even if there are not plans for a landline phone.
Jim Port is offline   Reply With Quote
Old 08-14-2008, 12:01 PM   #9
Ax grinder
raider1's Avatar
Yes, here is what the new section says:
250.94 Bonding for Other Systems.
An intersystem bonding termination for connecting intersystem bonding and grounding conductors required for other systems shall be provided external to enclosures at the service equipment and at the disconnecting means for any additional buildings or structures. The intersystem bonding termination shall be accessible for connection and inspection. The intersystem bonding termination shall have the capacity for connection of not less than three intersystem bonding conductors. The intersystem bonding termination device shall not interfere with opening a service or metering equipment enclosure. The intersystem bonding termination shall be one of the following:
(1) A set of terminals securely mounted to the meter enclosure and electrically connected to the meter enclosure. The terminals shall be listed as grounding and bonding equipment.
(2) A bonding bar near the service equipment enclosure, meter enclosure, or raceway for service conductors. The bonding bar shall be connected with a minimum 6 AWG copper conductor to an equipment grounding conductor(s) in the service equipment enclosure, meter enclosure, or exposed nonflexible metallic raceway.
(3) A bonding bar near the grounding electrode conductor. The bonding bar shall be connected to the grounding electrode conductor with a minimum 6 AWG copper conductor.
So you have 3 options, but each requires a bonding bar or set of terminals that permit at least 3 conductors to be connected.
Chris
Old 08-14-2008, 04:22 PM   #10
What is the best way you have found to install romex in exterior walls that are the styrofoam blocks/poly-steel?
Old 08-16-2008, 09:35 AM   #11
Before they insulate.
Old 08-16-2008, 11:54 AM   #12
Cut your grooves with a hot knife and secure with spray foam.
Old 08-16-2008, 01:18 PM   #13
The styrofoam is the insulation.
Old 08-16-2008, 08:47 PM   #14
Are you talking about the new walls that come pre-insulated? I know those have pre drilled holes for NM. But im not particulaly sure exactly what your talking about? We havn't came across it. At least the brazilians havnt done it yet anyways... haha.
Old 08-16-2008, 09:09 PM   #15
I've wired one of these things and are about to do another. I was just wondering if someone had a better method than the hot knife.
http://www.polysteel.com/construction.htm
Cut your own wood and it will warm you twice
Old 08-16-2008, 09:36 PM   #16
kbsparky's Avatar
Originally Posted by raider1 View Post
...So you have 3 options, but each requires a bonding bar or set of terminals that permit at least 3 conductors to be connected...
Chris
At least one jurisdiction that I know of is accepting 3 split-bolt bugs attached to your (#6 min) exposed section of the GEC.
The only problem I have with this is now it is more of a target to thieves, eyeballing the copper GEC, as well as those copper bugs attached to it.
Old 08-17-2008, 01:46 AM   #17
No Sh#t......... (must be what I'm doing wrong) Thats why you install before they install.
this is Called a "rough inspection" around here. If any insulation is installed before this inspection......... The insulators will have to do it twice.. three times, counting ripping it out.
Now has anyone else had this problem:
Inspector requireing derating? (mainly the blown in foam insulation)?
Beware, Itr's comming! 10s for your 20A ckt etc....
Had any problems with your phone/cable wires MELTING due to the HIGH heat of that stuff setting up?
Watch for that too.
Old 08-17-2008, 05:34 PM   #18
Have only done a few of these and used an electric chain saw, never have tried a hot knife.
TxElectrician is offline   Reply With Quote
Old 08-17-2008, 05:59 PM   #19
threewire's Avatar
You might want to find out if your state or county has adopted the 2008 code yet.
threewire is offline   Reply With Quote
Old 08-17-2008, 09:24 PM   #20
I never considered that. Probably a little messy but a narrow cut & fast which is nice. The fumes are pretty bad with the hot knife. I'll give it a try, thanks!
2008 code stillirnin NEC Code Forum 17 05-10-2008 07:39 PM
2008 code... waco General Electrical Discussion 27 04-17-2008 05:29 AM
2008 Code Changes gilbequick NEC Code Forum 40 01-19-2008 08:36 AM
AFCIs 2008 code waco General Electrical Discussion 18 12-30-2007 03:22 PM
2008 Life Safety Code Louieb Other Codes and Standards 1 04-27-2007 05:18 PM