Old 02-14-2017, 02:44 PM   #1
Moderator

 
Dennis Alwon's Avatar
 
Join Date: May 2009
Location: Chapel Hill, NC
Posts: 19,334
Rewards Points: 414
Default 210.52(e)

In the 2011 NEC, the outdoor outlets that are required at the front and back of one-family dwellings, and each unit of a two-family dwelling that is at grade level, were required to be accessible while standing at grade level. The 2014 NEC has deleted the phrase “while standing at grade level” and now requires the outdoor receptacle to be readily accessible from grade.

I had missed this change and boy that, IMO clearly allows us to mount a receptacle on a deck that is not more than 6'6" above grade to count as one of the two outdoor receptacles required by the code. This receptacle does not even have to be reached from grade just readily accesible and not more than 6 1/2' above grade. This means walking up the stairs of a deck would be compliant

Quote:
210.52(E) Outdoor Outlets. Outdoor receptacle outlets shall beinstalled in accordance with 210.52(E)(1) through (E)(3).
Informational Note: See 210.8(A)(3).
(1) One-Family and Two-Family Dwellings. For a one family
dwelling and each unit of a two-family dwelling that
is at grade level, at least one receptacle outlet readily accessible
from grade and not more than 2.0 m (6 1⁄2 ft) above
grade level shall be installed at the front and back of the
dwelling.
Dennis Alwon is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectricianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Sponsored Links
Advertisement
 
Old 02-14-2017, 03:36 PM   #2
Senior Member
 
MikeFL's Avatar
 
Join Date: Apr 2016
Location: The Sunshine State
Posts: 1,382
Rewards Points: 994
Send a message via Skype™ to MikeFL
Default

210.52(E) Outdoor Outlets. Outdoor receptacle outlets shall beinstalled in accordance with 210.52(E)(1) through (E)(3).
Informational Note: See 210.8(A)(3).
(1) One-Family and Two-Family Dwellings.

For a one family dwelling and each unit of a two-family dwelling that
is at grade level,

at least one receptacle outlet:

A. readily accessible from grade

and

B. not more than 2.0 m (6 1⁄2 ft) above grade level

shall be installed at the front and back of the dwelling.

That's how I read that.
__________________
Michael Gookin, President
GPS LightLock Astronomical Timers
www.GPSLightLock.com
(239) 848-6675
MikeFL is online now   Reply With Quote
Old 02-14-2017, 04:16 PM   #3
Senior Member
 
Signal1's Avatar
 
Join Date: Feb 2016
Location: Boston Area
Posts: 841
Rewards Points: 564
Default

From the commentary in the handbook.

"Outdoor receptacle outlets on decks porches and similar structures can be used to meet 210.52(E) as long as the receptacle outlet is not more that 6 1/2 feet above grade and be accessed by a person standing at grade."

There is also 210.52(E)(3) Balconies, Decks, and Porches. requiring a receptacle on decks that are attached to the unit, and accessible from inside the unit.
__________________
I can see Bunker Hill from my house!
Signal1 is offline   Reply With Quote
Old 02-14-2017, 04:18 PM   #4
Moderator

 
Dennis Alwon's Avatar
 
Join Date: May 2009
Location: Chapel Hill, NC
Posts: 19,334
Rewards Points: 414
Default

Quote:
Originally Posted by MikeFL View Post
210.52(E) Outdoor Outlets. Outdoor receptacle outlets shall beinstalled in accordance with 210.52(E)(1) through (E)(3).
Informational Note: See 210.8(A)(3).
(1) One-Family and Two-Family Dwellings.

For a one family dwelling and each unit of a two-family dwelling that
is at grade level,

at least one receptacle outlet:

A. readily accessible from grade

and

B. not more than 2.0 m (6 1⁄2 ft) above grade level

shall be installed at the front and back of the dwelling.

That's how I read that.
Mike they removed the words standing on grade for a reason.

Read this....
https://jadelearning.com/jadecc/cour...hp?imDif=651.1
Dennis Alwon is offline   Reply With Quote
Old 02-14-2017, 04:57 PM   #5
Senior Member
 
MikeFL's Avatar
 
Join Date: Apr 2016
Location: The Sunshine State
Posts: 1,382
Rewards Points: 994
Send a message via Skype™ to MikeFL
Default

Quote:
Originally Posted by Dennis Alwon View Post
Mike they removed the words standing on grade for a reason.

Read this....
https://jadelearning.com/jadecc/cour...hp?imDif=651.1
Thank you. That's well written.

If there were no stairway from the deck to grade then it would not count?

Or does it go farther that it's accessible by walking in the front door and out on to the deck?
__________________
Michael Gookin, President
GPS LightLock Astronomical Timers
www.GPSLightLock.com
(239) 848-6675
MikeFL is online now   Reply With Quote
Old 02-14-2017, 05:26 PM   #6
Senior Member
 
Signal1's Avatar
 
Join Date: Feb 2016
Location: Boston Area
Posts: 841
Rewards Points: 564
Default

Quote:
Originally Posted by MikeFL View Post
Thank you. That's well written.

If there were no stairway from the deck to grade then it would not count?

Or does it go farther that it's accessible by walking in the front door and out on to the deck?
I don't think so because then, it is not accessible from grade level.

Also if it's withing 25 feet of any outdoor HVAC equipment, this receptacle will satisfy the requirement of 210.63 provided it's at the same level.
I think we can assume the 6 1/2 feet here as well.
__________________
I can see Bunker Hill from my house!
Signal1 is offline   Reply With Quote
The Following User Says Thank You to Signal1 For This Useful Post:
MikeFL (02-14-2017)
Old 02-15-2017, 02:33 AM   #7
Deplorable-Electrician
 
MechanicalDVR's Avatar
 
Join Date: Dec 2007
Location: God's Country of Virginia
Posts: 27,866
Rewards Points: 25,080
Default

Quote:
Originally Posted by Dennis Alwon View Post
In the 2011 NEC, the outdoor outlets that are required at the front and back of one-family dwellings, and each unit of a two-family dwelling that is at grade level, were required to be accessible while standing at grade level. The 2014 NEC has deleted the phrase “while standing at grade level” and now requires the outdoor receptacle to be readily accessible from grade.

I had missed this change and boy that, IMO clearly allows us to mount a receptacle on a deck that is not more than 6'6" above grade to count as one of the two outdoor receptacles required by the code. This receptacle does not even have to be reached from grade just readily accesible and not more than 6 1/2' above grade. This means walking up the stairs of a deck would be compliant
One would think those that write these codes would be a little more specific in their wording!
MikeFL likes this.
__________________
I have never claimed to be a nice guy!

"Injustice anywhere is a threat to justice everywhere" mlk
MechanicalDVR is online now   Reply With Quote
Old 02-15-2017, 06:12 AM   #8
Moderator

 
Dennis Alwon's Avatar
 
Join Date: May 2009
Location: Chapel Hill, NC
Posts: 19,334
Rewards Points: 414
Default

Quote:
Originally Posted by MechanicalDVR View Post
One would think those that write these codes would be a little more specific in their wording!

I agree but as a person that has written proposals, I will tell you that it is difficult. You are free to write a proposal to any section of the code that you believe needs clarification.
Dennis Alwon is offline   Reply With Quote
Old 02-15-2017, 06:20 AM   #9
motherplucker
 
chicken steve's Avatar
 
Join Date: Mar 2011
Location: the Green Mountain state
Posts: 34,935
Rewards Points: 5,228
Default

As an aside, we had even more fun with an archy dictating receptacle outlets along an ADA ramp. Unfortunately the HD covers he spec'd stuck out 2" into the 'ADA area'. Lot's of fun when one has 'dueling codes' .....~CS~
chicken steve is online now   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



All times are GMT -4. The time now is 12:30 AM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.1
vBulletin Security provided by vBSecurity v2.2.2 (Pro) - vBulletin Mods & Addons Copyright © 2017 DragonByte Technologies Ltd.
User Alert System provided by Advanced User Tagging (Pro) - vBulletin Mods & Addons Copyright © 2017 DragonByte Technologies Ltd.
Our Pro Sites Network
ContractorTalk.com | DrywallTalk.com | HVACSite.com | PaintTalk.com | PlumbingZone.com | RoofingTalk.com