Old 02-26-2011, 11:10 PM   #1
Default ampacity
What size aluminum SER cable do you need to feed an 100 amp sub panel in a residence?
yetti is offline   Reply With Quote
Old 02-26-2011, 11:43 PM   #2
Heavily Armed Member
HARRY304E's Avatar
Take a look at 310.15(B)(7) table...#4 copper..
Welcome to the forum you will have fun here and learn something too...
Old 02-26-2011, 11:44 PM   #3
erics37's Avatar
He said aluminum, Harry
- Eric
erics37 is online now   Reply With Quote
Old 02-27-2011, 12:08 AM   #4
That table only applies if the panel is on the main feeder to the unit.
Old 02-27-2011, 05:14 AM   #5
BBQ
BBQ's Avatar
Harry is drunk.
Depending on which year NEC you are on (and your main service conductor size) #1 AL or 1/0 AL.
Old 02-27-2011, 02:10 PM   #6
NRA Member
backstay's Avatar
[quote=yetti;392197]What size aluminum SER cable do you need to feed an 100 amp sub panel in a residence?[/quote
Table 310.15(B)(7) for full unit(as an apartment)
Old 02-27-2011, 02:14 PM   #7
BBQ
BBQ's Avatar
Table 310.15(B)(7)
#2 AL
In most cases you cannot use Table 310.15(B)(7) to supply a sub panel, you would have to use Table 310.16.
Old 02-27-2011, 02:18 PM   #8
NRA Member
backstay's Avatar
So the question is, what is the sub panel feeding, an apartment or a guest house or a panel to add spaces for expansion?
Old 02-27-2011, 02:21 PM   #9
NRA Member
backstay's Avatar
The 2011 book has no 310.16 anymore, table is 310.15 now. Our continuning ed classes are on the 2011 NEC now.
Old 02-27-2011, 02:28 PM   #10
Read 310.15 (B)(6) in the 08 code they clarified that the use of table 310.15(B)(6) only applies to conductors carrying100% of the dwellings deversified load.
Mr Rewire is offline   Reply With Quote
Old 02-27-2011, 02:30 PM   #11
BBQ
BBQ's Avatar
Thanks, I have the 2011 beside me but did not notice 310.16 was now .15
Old 02-27-2011, 03:00 PM   #12
Not exactly, what was T310.16 is now 310.15(B)(16). All of the ampacity tables are 310.15(B)(xx), with the xx being the .(xx) in the 2008 code.
Old 02-27-2011, 03:26 PM   #13
And ya'll wonder why some people (like me) can't recite codes!
racerjim0 is offline   Reply With Quote
Old 02-27-2011, 03:30 PM   #14
Fried Bologna um um good!
jwjrw's Avatar
He asked what size SER he would need to run for a sub panel. BBQ had it correct. 1/0 is good for 100A at 60 degrees.
Old 02-27-2011, 05:41 PM   #15
I'm sorry, while I realize this is the true code today, for YEARS we ran #2AL SER to a sub-panel. It is (still) good enough for a main feeder, yet it is more than two sizes to small today for a sub-panel. Pathetic.
Anyone EVER hear of ANY issues with running #2AL SER to a 100A sub-panel???? Grrrr.
Oh well, live by the code, I know.
Old 02-27-2011, 06:04 PM   #16
HARRY304E's Avatar
Harry is drunk.
Mabe i was..
Old 02-27-2011, 11:45 PM   #17
Thanks for all the input, I am going off of 2008 code, and the sub-panel does supply 100% of the dwelling units load, so it is considered the main feeder. So according to 310.15(B)(6) I am allowed to use a #2 XHHW SER CABLE to feed the panel with 100 amps.
Old 02-28-2011, 02:43 AM   #18
HARRY304E's Avatar
Yes that is right if you are going by the 2011 NEC it would be table 310.15(B)(7) That is the only differnce..
14 AWG allowable ampacity shocking NEC Code Forum 31 05-09-2013 04:11 PM
Ampacity Derating switchleg Residential Electrical Forum 35 11-23-2009 10:20 PM
cable ampacity waco General Electrical Discussion 3 03-26-2009 08:59 AM
What is the ampacity for 8 AWG wire? 50 or 40 gilamor NEC Code Forum 23 10-19-2008 09:28 PM
ampacity waco General Electrical Discussion 3 08-15-2008 05:26 PM