Originally Posted by rewire
Size your OCP device frst based on 215.3 then select your conductor using the 74C column based on the calculated load now apply your derating factors if the selected conductor after derating cannot be protected by the OCP device then select the next size wire at this point you can use the 90c table for derating.You size the OCP device then find the wire size based on 75c
Thanks a million, Rewire. I must say that your explanation is far clearer than is either my textbook or the NEC. According to your recipe, then, the correct solution is:
step #1: OCPD = 350 A based upon next standard size above the calculated load
step #2: using 75 degree C column in conjunction with calculated load, 325 A, I observe that 400 kcmil conductors are required.
step #3: derate using the 90 degree ampacity:
allowable ampacity = 380 A X 0.91 = 345.8 A, which is substantially greater than the true load.
This conductor may, in fact, be protected by a 350 A OCPD, so the problem is solved.
The correct answer is therefore 400 kcmil, as 50% of my classmates insisted.
Thanks again for a great explanation.