2-142 Log #3488 NEC-P02 Final Action: Accept
(210.12(B))
__________________________________________________ __________
Submitter: Alan Manche, Square D Co.
Recommendation: Revise 210.12(B) as shown below:
(B) Dwelling Units. All 120-volt, single phase, 15- and 20-ampere branch
circuits supplying outlets installed in dwelling unit s bedrooms shall be
protected by a listed arc-fault circuit interrupter, combination type installed to
provide protection of the branch circuit. Branch/feeder AFCIs shall be
permitted to be used to meet the requirements of 210.12(B) until January 1,
2008.
Substantiation: For the past three NEC cycles, CMP 2 has reviewed extensive
amounts of data and information pertaining to the benefit of AFCIs for the
protection of dwelling unit branch circuits. After careful consideration the
panel decided to required AFCIs on branch circuits that supplied bedrooms as a
means to gain experience and to put the application in an easily defined area.
AFCIs have had an excellent track record in the field and their installation/use
have found numerous wiring errors and in addition they have found wiring
damage and equipment damage that could have been potential sources of fire.
With the experience gained, it is an appropriate time to expand AFCIs to all 15
and 20 ampere branch circuits in the dwelling. There is no basis for limiting the
protection to circuits that supply only bedrooms and the increased protection is
needed for other circuits. This expansion will continue the effort to address
fires of electrical origin in dwellings.
The text has been modified to apply to all 120V 15 and 20 ampere branch
circuits that supply outlets in all locations. The second paragraph is proposed to
be deleted since it is no longer applicable.
Panel Meeting Action: Accept
Number Eligible to Vote: 12
Ballot Results: Affirmative: 8 Negative: 4
Looks to me that it has been accepted in this one already. Guess that means in the year 2020 when MD's area adopts the 2008 code it's a go.