ATS Sizing Question - Electrician Talk - Professional Electrical Contractors Forum
Old 12-16-2010, 07:46 AM   #1
Default ATS Sizing Question
We are going to install a service entrance ATS with a utility disconnect switch MCCB, input power coming from utilities 13.8KV secondary trafo of 220Vac,3Ph and from 200KVA,3Ph, 525 Ampere generator
Downstream is a 2 x 30KVA AC UPS (parallel Redundant) to supply power to the plants SCADA Control Room.(max.load in the room)
The engineer incharge for this project (client side) ask for a 400A service entrance ATS(with a utility disconnect switch MCCB), however i find it too big for its total load requirement (assumming UPS full load of 60kVA/72KW [p.f=0.8])
generally i would size the ATS rating using [Total System Load] divided by [square root of 3]*[220V] = 72,000 / 381 = 189 Ampere, hence i would say 200 Ampere Service Entrance ATS is more suitable.
Am i correct with my sizing calculation? if im wrong, please advice me correct sizing calculations.
what will be the effects if we use the 400A SE ATS??? technical issues???
advice?anyone?
thanks......
Eulem_sa is offline   Reply With Quote
Old 12-16-2010, 08:20 AM   #2
Semper Fidelis
Suncoast Power's Avatar
Rewards Points: 3,472
I am sorry but that was kind of hard to follow.
At what point are you installing the ATS??
or just enjoy the show.
Old 12-16-2010, 09:16 AM   #3
Rewards Points: 132
Let me preface this by saying I know very little about generators but IMO, a load of 189 amps may be too much for a 200 amp ATS. Is the 189 a,ps continuous load? Is the ATS rated for 100% of a continuous load?
Old 12-16-2010, 09:36 AM   #4
Semper Fidelis
Is the price or the physical size the issue?
Old 12-16-2010, 12:27 PM   #5
Default Size
تحتاج إلى حجمه في 125 ٪ من تحميل الخاص المستمر. لماذا أنت هنا يكمن في
BobBob is offline   Reply With Quote
Old 12-18-2010, 04:01 AM   #6
Default ATS Sizing question
if i rate the ATS at 125% of the total system load of 200A then it will give me a 250A rating.
If i will go ahead and use the 400A rating are there gonna be any technical issues to arise?
Do i have to consider the generators ampere rating as it gives 525A at continous load.
if so then i would be needing atleast 600A SE ATS rating, am i correct?
Old 12-18-2010, 09:26 AM   #7
Rewards Points: 600
Standard size for MOST ATS manufactures would be a 200, 230 or 260.
Old 12-21-2010, 11:34 AM   #8
Rewards Points: 250
didnt you say the generator is 525 amps?
Control Freak is offline   Reply With Quote
sizing mbj highlandele Commercial Electrical Forum 6 09-23-2010 02:07 PM
sizing the neutral jpimentel84 General Electrical Discussion 6 09-02-2010 07:38 PM
Generator Sizing Mountain Electrician General Electrical Discussion 23 06-03-2008 07:08 AM
concuctor sizing Bkessler General Electrical Discussion 4 03-02-2008 07:41 PM
transformer sizing ???? Vr_ecobox Services and Service Equipment 1 12-07-2007 08:49 PM