02-28-2008, 06:45 PM
S.E. Training Manager
Bare Ground in EMT?
It has recently been interpreted by an AHJ in FL that pulling bare copper ground wire in metal conduit is a code violation. We have asked for a code reference, but I suspect it will be 342.14 , 344.14, or 358.12(6).
If anyone knows of any code reference that would contradict this ruling, please let me know your input.
02-28-2008, 07:03 PM
Ax grinder
So how would running a bare copper ground wire in a steel conduit be any different than attaching a copper EGC at a steel box?
There is no prohibition in the NEC to installing a bare copper EGC in a steel conduit.
Take a look at 250.118(1) this section specifically permits a bare copper conductor to be used as an EGC.
Chris
02-28-2008, 08:36 PM
so you can use a bond bushing to make sure that the conduit is bonded, but the bare copper isn't allowed ? wtf ?
02-28-2008, 11:49 PM
What is the conduit/circuit being used for?
Dave
02-29-2008, 12:15 AM
I believe that the above stated sections have to do with dissimilar metals as related to aluminum and copper connected together which will cause a galvanic action not a copper ground wire coming in contact with metal conduit.
A bare EGC in conduit is a bit uncommon trade practice though.
02-29-2008, 12:21 PM
This is true, we have to wrap our conduits if they come into to close of contact with copper plumbing pipes.
02-29-2008, 08:22 PM
we have them wrap the copper.
is it al conduit?
03-01-2008, 08:08 AM
Wish I was in the water
Which county did this, Orange or Seminole?
If you're gonna be stupid, you better be tough.
03-01-2008, 07:21 PM
Palm Beach County is where the site is.
03-03-2008, 10:33 AM
is it al conduit?
Yeah, you can wrap either the copper or conduit as long as they don't touch.
03-03-2008, 04:31 PM
I use bare copper in conduits all the time. Mostly to run to the ground rod when there is a house on a slab and I am doing a service change.
When ls lunch
03-04-2008, 10:43 AM
I was taught not to do this because the conduit would act as a choke and inhibit the path to ground.
03-04-2008, 11:12 AM
Ax grinder
If you bond both ends of the conduit to the GEC then you are OK. (See 250.64(E))
It is better to use a non-ferrous raceway to enclose the GEC such as schedule 80 PVC.
Chris
03-04-2008, 11:39 AM
This seems like a better game plan to me.
03-05-2008, 09:36 AM
maybe this is the way I will do it from now on with pvc.
When ls lunch
03-05-2008, 10:22 AM
Ax grinder
I always use PVC to run my GEC, it eliminates all of the problems with electromagnetic fields and the chock effect around the GEC.
Chris
10-14-2009, 08:16 PM
Bare ground wires
I have gotten my butt ripped about power factor, so I am not afraid of this one. Someone in Florida is thinking that if you run a bare "Equipment grounding conductor" in EMT you are definitely creating a parallel path of fault current, if a fault current exists. The problem is when the (parallel path of fault current is interrupted by a BREAK, as a loose, or non existent tight coupling. Theoretically, at the point of the (LOST) connection in the conduit, an Inductive choke could be developed and an IMPEDENCE is set up as to restrict the FAULT CURRENT, and slowing the tripping of the overload device which would be measured in cycles per second. That is my story and I'm sticking to it.
RIVETER
10-14-2009, 10:40 PM
#18
RIVETER does the fault current cause this BREAK? Or was this BREAK a pre-existing condition?
10-14-2009, 11:16 PM
#19
Fault current
You are correct, the break is a pre- existing condition.
NOT THE FAULT.
Reason: wRONG WORD
10-15-2009, 07:58 AM
#20
Originally Posted by RIVETER
You are correct, the fault is a pre- existing condition.
So what happens when one the hack electricians leaves the copper connection loose? The argument some use of loose connections can be applied to any thing we do. I say if that is the quality of work you do or are use to sub it all out to professionals.
I can argue that all wiring should be in rigid for the same reason. A hack electrician improperly installs NM and nicks the insulation, better use rigid.
So the point is when properly installed there is no issue, if you cannot properly install it hang drywall.
I void warranty's
| Thread |
Thread Starter |
Forum |
Replies |
Last Post |
2 ground rods
MikeD |
NEC Code Forum |
116 |
12-07-2009 12:38 PM |
Ufer ground
James Con |
14 |
12-04-2009 08:45 PM |
Counterposing Ground
casparbrooke |
6 |
07-31-2008 07:50 PM |
Equipment Ground
Absolutetruthz |
6 |
06-06-2008 06:23 AM |
Ground or not to ground?
chenley |
Services and Service Equipment |
5 |
05-06-2008 11:38 PM |