Old 09-21-2010, 09:17 PM   #1
Default Bonding GEC to neutral
Can you bond the GEC to the neutral on a jumpered bus. Example would be you land your neutral on a bus then run a jumper to your ground bus and land your GEC on the ground bus. I read through 250 and I didn't see where it says you can't do this. Want to make sure I'm not missing something.
Old 09-21-2010, 09:36 PM   #2
You should bond the GEC to the neutral. The best way to insure that is to land them on the same buss. It does not say to insure that the GEC and the Neutral are at the same potential...even though they are.
Old 09-21-2010, 11:50 PM   #3
goose134's Avatar
I got pinched on this. It wasn't a big deal to change, but I was never cited a reference. Why did you have to do this?
A professional in an amateur world.
Old 09-22-2010, 12:02 AM   #4
I always land on the same bus just because.. but had a apprentice that landed a GEC on a seperate bonded bus. I wasn't sure if it was legit or not. Not overly concerned but like to know if the NEC allows this. I couldn't find anything prohibiting it.
Old 09-22-2010, 04:26 AM   #5
Fried Bologna um um good!
jwjrw's Avatar
If it is sized to carry the fault current you can. I usually run a #4 or #6 if I'm in a situation where it is necessary to do that. Sometimes its the easiest / fastest way to go.
Old 09-22-2010, 01:17 PM   #6
Ax grinder
raider1's Avatar
Take a look at 250.24(A)(4).
Where the main bonding jumper specified in 250.28 is a wire or busbar and is installed from the grounded conductor terminal bar or bus to the equipment grounding terminal bar or bus in the service equipment, the grounding electrode conductor shall be permitted to be connected to the equipment grounding terminal, bar, or bus to which the main bonding jumper is connected.
Chris
The Following 3 Users Say Thank You to raider1 For This Useful Post:
I_get_shocked (09-22-2010), jwjrw (09-22-2010), nitro71 (09-22-2010)
Neutral Up or Down ? user438 General Electrical Discussion 15 05-14-2010 07:15 AM
No neutral BIGRED General Electrical Discussion 34 03-19-2010 11:34 PM
one leg 130v to neutral the other 117v to neutral??? brooklyn General Electrical Discussion 3 01-07-2010 07:59 PM
120 v in neutral??? lamino69 General Electrical Discussion 10 01-14-2008 09:34 PM
Neutral? brian john NEC Code Forum 14 04-10-2007 11:55 AM