Bonding/Grounding yellow flexible gas line??? - Electrician Talk - Professional Electrical Contractors Forum
Old 12-09-2009, 09:08 PM   #1
Default Bonding/Grounding yellow flexible gas line???
Has anyone had any experience in having to bond the yellow flexible gas line to the electrical ground???? I had a call from my plumber buddy today asking if we could bond his gas lines on the roof of a commercial building. I know you have to bond with a ground clamp each section of flex line that is broken by a fitting but i am not sure what size wire we need and if we can just take it to a grounding conductor in a nearby circuit or if we need to take it all the way back to the grounding electrode??
Thx for the help guys!
abond82 is offline   Reply With Quote
Old 12-09-2009, 09:12 PM   #2
william1978's Avatar
Rewards Points: 2,000
You will have to install it per manufactors instructions. Ask your buddy for the instructions all the info you will need is on there.
Old 12-09-2009, 09:15 PM   #3
Instructions on what???? the spool of flex gas line? didnt think it came with instructions.
Old 12-09-2009, 09:17 PM   #4
The instructions on the CSST gas pipe.
Old 12-09-2009, 09:18 PM   #5
OK?????
have you ever done this before? We dont have instructions for the gas line.....
Old 12-09-2009, 09:20 PM   #6
OK?????
I bet I have seen instructions for CSST about 150 to 200 times. The inspector won't ask for them?
Old 12-09-2009, 09:21 PM   #7
evil bastard
mcclary's electrical's Avatar
Rewards Points: 746
If it's black iron, it's considered bonded by the EGC. But if there's any CSST on the whole job, even a short piece somewhere, it requires a #6 bond to the service panel or subpanel. The bond should be within 5' of the pipe entering the building. You do not have to bond each flexible piece of CSST. In fact, you NEVER put a clamp on the CSST. It goes on the black pipe. A #6 will pass inpection in 99% of places and manufacturers. However, one manufacturer (I think wardflex) demands a bond to be the same size as the GEC, I got caught on that one time, and had to change a #6 bond to a #4 bond (200 amp service)
Old 12-09-2009, 09:25 PM   #8
He is doing it on a commercial building this wire could end up being pretty big. The wire doesn't have to go back within 5'. You can hit it any where there is ridged gas pipe or you can hit the manifold.
Old 12-09-2009, 09:32 PM   #9
evil bastard
Rewards Points: 746
I've had more than one inpsector ask for the bond to be within 5' and yes, on a big service, with wardflex CSST, it would be a big bond.
Old 12-09-2009, 09:35 PM   #10
Did he tell you why he was wanting it within 5'? I'm just wondering thats all. I might be wrong, but I don't think it does maybe Dennis will look at this thread I believe he does alot of house's.
Old 12-09-2009, 09:44 PM   #11
evil bastard
Rewards Points: 746
He basically said so peolle will know it's there. I actually don't think the 5 foot rule is written anywhere, merely copying the GEC rule. A bond anywhere IMO would be fine. But, it is required to be accessible, so right where the pipe goes through the wall usullally works good.
Old 12-09-2009, 09:48 PM   #12
I just found an interesting web site.
It states that per NEC you look at 250.104 (B). this talks about "other metal piping". This says that you have to bond the piping per the size ground that is supplying the circuit that could energize the pipe.
You guys are both correct though in the fact that the #6 is the new standard that will probably be adopted to NEC and is what the manufacturers recommend
Now in my case the main gas line is black iron but on the roof it changes to flex to feed the Heat units. Do I only need to bond the main gas line at the service with a #6 or whatever size the GEC is?
Old 12-09-2009, 09:51 PM   #13
Rewards Points: 272
Some manufacturers require a #6 bond back to the service while others require you to use T.250.66 to size it. The clamp cannot be attached to the yellow pipe but rather to the brass fittings that connect the pipes.
Usually we have a short section of black iron and the other pipe is connected to that. In that case I have connected to the black pipe.
Old 12-09-2009, 09:55 PM   #14
evil bastard
Rewards Points: 746
99.9 % of the time, a #6 is all you need. There is only one man. (that I know of) that requires the bond to be the same size as the GEC. Bond the black pipe to the service with a #6 is all you need. The NEC has not adopted the yet. The 2006 IRC has already adopted it. That's how it's enforced here. The USBC is next in line to adopt it on there next cycle. They both mandate a #6.
Old 12-09-2009, 09:56 PM   #15
I knew you would show up Dennis.
Old 12-09-2009, 10:28 PM   #16
Rewards Points: 2,062
Honestly, I have never had to bond any CSST. But If I were to be charged with the task of bonding such a system effectively, I think I would stick a country clamp on each piece of black pipe where the CSST terminated, and run a #6 between each fitting and eventually back to a panel, or building steel, or a copper water line, in a commercial setting.
Old 12-09-2009, 10:41 PM   #17
How would you make any money doing all of that? I don't think you would win the bid.
Old 12-09-2009, 10:45 PM   #18
Well, if they wanted it done, they will have to pay for it. Otherwise I just keep on keepin' on. I don't bond or touch any gas line unless it is required by local code for me to do something special to it. One single piece of #6 run through a building hitting bond clamps at various CSST terminations, would likely be relatively inexpensive.
Old 12-09-2009, 10:48 PM   #19
On some of the houses around here those that wire houses where charging $200 to bond the gas pipe. Not me.
Old 12-09-2009, 10:51 PM   #20
Rewards Points: 2,012
??? Just a thought, As soon as you plug in or wire any gas appliance,Isn't it bonded?
I have never been asked or questioned about it.
250.104(2)B. .. (Para phrase) The bond Jumper to be sized to the ckt that is "Likely to energize the piping system".
"The equipment grounding conductor for the ckt that is likely to energize the piping shall be permitted to serve as the bonding means. The point of attachment of the bonding jumper(s) shall be accessible."
What is the ckt most likely to energize the equipment?
grounding and bonding george nicholson General Electrical Discussion 1 01-29-2010 11:51 AM
grounding vs bonding????? stillirnin NEC Code Forum 11 04-18-2009 09:58 PM
Bonding the water line. k2x General Electrical Discussion 9 08-15-2008 06:30 PM
grounding & bonding question bigredc222 Services and Service Equipment 35 02-29-2008 08:00 PM
Grounding and bonding a transformer Jim Workplace Safety 5 08-18-2007 09:08 PM