Bonding lock nut vs grounding bushing - Electrician Talk - Professional Electrical Contractors Forum
Old 04-25-2011, 05:21 PM   #1
Rewards Points: 2,000
Default Bonding lock nut vs grounding bushing
Is there any application difference when your conduit is ran into a steel can? I'm thinking.. no?
Old 04-25-2011, 05:34 PM   #2
Rewards Points: 472
This is from the UL book
[COLOR="rgb(139, 0, 0)"]Grounding and Bonding Bushings [/COLOR]— Bonding bushings for use with
conduit fittings, tubing (EMT) fittings, threaded rigid metal and intermediate metal conduit, or unthreaded rigid metal and intermediate metal conduit are provided with means (usually one or more set screws) for reliably bonding the bushing (and the conduit on which it is attached) to the metal equipment enclosure or box. They provide the electrical continuity required
by the NEC at service equipment and for circuits rated over 250 V. Means for connecting a grounding or bonding conductor are not provided and if there is need for such a conductor a grounding bushing should be used.
Grounding bushings for use with conduit fittings, tubing (EMT) fittings, threaded rigid metal and intermediate metal conduit, or unthreaded rigid metal and intermediate metal conduit have provision for the connection of a bonding or grounding wire or have means for mounting a wire connector available from the manufacturer. Such a bushing may also have means (usually
one or more set screws) for reliably bonding the bushing to the metal equipment enclosure or box in the same manner that this is accomplished by a bonding bushing. Grounding bushings provide the electrical continuity required by the NEC at service equipment and for circuits rated over 250 V.
They may be used with or without a bonding or grounding conductor as determined by the bonding or grounding function that is intended to be accomplished. Insulating throat liners in grounding or bonding bushings are suitable for temperatures of 150C if they are black or brown in color. Unless otherwise marked, insulating throat liners of any other color are suitable for temperatures of 90C.
Grounding and Bonding Locknuts — Grounding and bonding locknuts serve in a manner similar to grounding and bonding bushings except they do not provide abrasion protection for the conductor at the end of the conduit.
bonding bushing flip250r General Electrical Discussion 11 03-30-2011 03:25 PM
grounding bushing needed?? ohiosparky99 General Electrical Discussion 3 11-12-2010 08:32 PM
Bonding and Grounding leo NEC Code Forum 6 01-29-2010 11:26 AM
grounding vs bonding????? stillirnin NEC Code Forum 11 04-18-2009 08:58 PM
Concentric KO and when to use Grounding bushing Losrod General Electrical Discussion 29 07-11-2008 10:21 PM