12-11-2008, 10:02 PM
Branch circuit conversion - grounded conductor?
We have an existing 227/480v 75amp circuit servicing a 20 ton chiller (no grounded conductor). Our client wants to demo the chiller and convert the existing circuit to a feeder to power a sub panel. This new panel will only power 3 motors (5 hp each, 480v 3 phase). Does the NEC require that we pull in a grounded conductor to comply? And where in the code is this located?
12-11-2008, 10:35 PM
Originally Posted by Batas
We have an existing 227/480v 75amp circuit servicing a 20 ton chiller (no grounded conductor). ....
So is it 480v (no grounded conductor, or 480/277 (which DOES imply a grounded conductor)
John from Baltimore
"One day at a Time"
12-11-2008, 11:33 PM
The existing branch circuit supplying the 20 ton chiller does not have a grounded conductor. . . .
12-11-2008, 11:42 PM
Burger Flipper
Neutral is not required to be present if you do not have any loads requiring it to be there.
~Matt
12-12-2008, 05:40 AM
Does it have an equipment grounding conductor?
Rick Boudreau
Al Asad, Iraq
12-12-2008, 09:40 AM
Yes. . . .
12-12-2008, 09:51 AM
Not Banned Yet
Is there an echo in here?
March 2010: On the road with my RV. California is first primary destination then it is off to Eastern OR, Northern ID and Western MT for drycamping and fly fishing until Labor Day.
12-12-2008, 10:42 AM
I was asking about the equipment grounding conductor not the grounded condcutor that it was already stated is not present. The equipment grounding conductor was not mentioned prior to my post.
If the equipment grounding conductor is present, and the GROUNDED conductor is not needed there is no reason to install it.
Rick Boudreau
Al Asad, Iraq
12-24-2008, 12:19 PM
480/277
If the equiment is 480/277 then you should have all the conductors you need plus one extra (3phase, 1grounded, 1ground), if you have a 480V connection you would still have 3phase conductors plus a ground so you should have the applicable wiring avaliable, another item not knowing the in's and out's of the installation what about bonding the conduit (if not already done so) provide a bonding bushing at each end and use th conduit as a ground path?
11-09-2009, 03:31 AM
yah i agree w/you
11-09-2009, 06:16 AM
The bonding bushing is not required unless you're going into eccentric KO's. You can't have 277 without a grounded conductor. But if your loads do not require it, you do not have to run it.
11-09-2009, 06:25 PM
Chairman of the Bored
Originally Posted by angelito
yah i agree w/you
I beat Billy to this one:
Welcome to forum.
11-09-2009, 06:47 PM
Licensed Journeyman
yah i agree w/you
welcome to the forum