Default Class II Division 2

I am having a little trouble with article 502. Can I install a dust tight (nema 4X) junction box for splices? I understand it that the box needs threaded hubs to enclose a splice. But others are telling me splices can be made in the 4X enclosure. BTW this is group F.

dawgs is online now   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectricianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Old 12-14-2009, 09:10 PM   #2
animal lover /rat bastard
 
wildleg's Avatar
 
Join Date: Apr 2009
Location: central east coast us
Posts: 9,182
Send a message via ICQ to wildleg
Default

I believe that is correct. 502.10 B 4. The assumption is that group F is correct. there are several articles that say that if other dusts are present that the box has to be listed for div 2 (its good to read thru the whole thing a few times)

__________________
As President Roosevelt said: "We have nothing to fear but fear itself. And Chuck Norris. And 滿口胡言. And Grabthar's hammer. And Gort. and 江南 Style. and rotting in the street and Zombies . . . and Wayne Griffen "
wildleg is online now   Reply With Quote
Old 02-02-2010, 01:07 PM   #3
Junior Member
 
Join Date: Feb 2010
Location: kentucky
Posts: 2
Default

i agree with wildleg. if you look in a hoffman book under hazerdous locations it states that cl 2 div 2 nema type 3, 4, 4x, 12, 12k, and 13 are considered dust tight
edginter is offline   Reply With Quote
Old 01-11-2013, 11:05 PM   #4
Junior Member
 
Join Date: Jan 2013
Location: Central Illinois
Posts: 2
Default

This is the way I interpret the code, but I also think a gasketed, malleable, form 35 Appleton conduit fitting is dust tight. Let me know what you think?
RARJ60 is offline   Reply With Quote
Old 11-22-2013, 03:24 PM   #5
WMF
Junior Member
 
Join Date: Nov 2013
Location: VA
Posts: 1
Question Class II Div II recep's in cabinet shops

I've been reading a lot on article 502-115 &502-145, and speaking to the local authorities on the requirement for receptacles around wood working equipment. The shop in question has a very large dust collection system, and a standard cleaning system in place. The owner has paid an engineer to decide what classification it will be. They are calling it Class II Div II group G, My question is do I have to use explosion proof receptacle or do they make something more affordable to the owner. I plan on hardwiring most of the equipment but you still have general use receptacles thru out the shop. And being that it is a shop and you are standing on concrete do they need to be GFI.
WMF is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
PLC Online Class ricoreece1 PLCs, VFDs, Motors and Controls 19 03-18-2014 08:22 AM
class 1 division 1 hazardous location NolaTigaBait NEC Code Forum 43 12-08-2009 12:23 PM
Creating a Service Division GrumpyRoofer Business, Marketing, and Sales 26 08-27-2009 10:52 AM
Class II Division I??? gilbequick NEC Code Forum 10 11-21-2008 09:14 PM
class 1 div 1 HCECalaska General Electrical Discussion 9 03-28-2007 04:46 PM


All times are GMT -4. The time now is 09:53 AM.


Copyright 2006-2014 Escalate Media LP. All Rights Reserved
Our Pro Sites Network
ContractorTalk.com | DrywallTalk.com | HVACSite.com | PaintTalk.com | PlumbingZone.com | RoofingTalk.com