11-05-2009, 06:24 PM
Copper pipe used in place of emt?
Was at an apartment building today, we are doing the lighting, fire alarms, exits, surveilance etc and associated conduit.
Was in the electrical room rolling back the wire from the temp panel and all of the existing panels had copper tubing running into all of the different panels.
Building is from the 50s
the bends looked like they were done by hand, like the panels had dreads coming out of them. It looked really bad
Curious if this was common place in the past? What had me curious was that the main disconnect was fairly new and had the most copper pipe running into it
11-05-2009, 06:28 PM
Umm that's not copper pipe that's Pyrotenax. They loved that stuff back then haha
Still lots of it being installed for special applications. I ran some 2 weeks ago!
11-05-2009, 06:29 PM
semi-electrician
Copper has always been more costly than steel, so I don't see any good reason to have used copper. I have seen heavy brass pipe used in old homes more than once, never knew why they used it.
11-05-2009, 06:32 PM
Unlimited Lic.Electrician
Are you sure it wasn't MI cable?
11-05-2009, 06:35 PM
ahhh
this is exactly what it looked like;
interesting!
11-05-2009, 06:38 PM
Do you have a picture of the inside of the panel?
11-05-2009, 06:42 PM
It's a pain in the a$$ to work with, but it really is such a great product.
11-05-2009, 06:45 PM
Are you talking about copper or MI?
11-05-2009, 06:46 PM
semi-electrician
So what is great about it?
11-05-2009, 06:51 PM
The fire rating, and it is tough as hell. We use it for all emergency power feeds in some hospitals for fire pumps and very critical loads as it has a 2 hour fire rating.
Also popular for explosion proof areas.
11-05-2009, 06:55 PM
They use it for some fire pumps around here, because of the 2-hour rating. Are you talking about MI cable?
11-05-2009, 06:58 PM
ahhh
interesting!
That's MI cable, not copper tubing.
11-05-2009, 06:59 PM
Originally Posted by EBFD6
That's MI cable, not copper tubbing.
I agree.
11-05-2009, 07:28 PM
Yep I am talking about MI cable....we call it Pyrotenax
11-05-2009, 07:30 PM
Ok, we are on the same page.  I have just not ever heard it called that before. Thanks for clearing that up.
yeah, i searched up MI cable to get that photo. I had mistakenly thought it was copper tubing
11-05-2009, 07:35 PM
Either way it should be a learning experience. I don't know about the others but its not every day you get to work around MI cable.
11-05-2009, 07:38 PM
#18
Some of us have never worked it!
GO JACKETS!
11-05-2009, 07:55 PM
#19
I see a lot of it in hospitals...usually in retrofits. You see a lot of pyro being used for fire alarm devices in larger buildings and for cold leads for heat tracing cables.
You need to be pretty skilled at terminating it, if you mess up you are done for!
11-05-2009, 07:59 PM
#20
Hopefully one day you will get a chance to work with it.