Old 04-17-2012, 11:00 PM   #1
Cletis's Avatar
Default De-Rating
Can I put 3 sets (parallel) of 208 Wye system 250mcm/250mcm/250mcm/1/0 in a 4" Rigid Metal conduit for a 500 amp service ?
www.cletiselectric.com
Cletis is online now   Reply With Quote
Old 04-17-2012, 11:02 PM   #2
Ninety's Avatar
With or without soap?
Ninety is offline   Reply With Quote
Old 04-17-2012, 11:03 PM   #3
Cletis's Avatar
Default wo
Without. Simpull Al
Old 04-17-2012, 11:10 PM   #4
Awg-Dawg's Avatar
500 Amp?
I'm just hoping to not end up on Electricmanscotts signature line.
Awg-Dawg is offline   Reply With Quote
Old 04-17-2012, 11:36 PM   #5
Cletis's Avatar
Default ?
Originally Posted by Awg-Dawg View Post
500 Amp?
Yeah. Anything wrong with that? Let's say I had a calculated load of 467 amps
Old 04-17-2012, 11:38 PM   #6
Awg-Dawg's Avatar
No.
Ive just never seen a 500 amp service.
Old 04-17-2012, 11:42 PM   #7
Cletis's Avatar
Default me
No.
I'm a trendsetter..
Old 04-17-2012, 11:45 PM   #8
Awg-Dawg's Avatar
I'm a trendsetter..
Clearly, that has never been questioned
The Following User Says Thank You to Awg-Dawg For This Useful Post:
dronai (04-17-2012)
Old 04-18-2012, 12:09 AM   #9
Awg-Dawg's Avatar
Is this a homework question?
Old 04-18-2012, 02:09 AM   #10
If I read your post correctly you will have 9CCC and 3non CCC in one 4" RGS conduit. Thats 12 cables in the one conduit,,,,,,How many guys going to pull the wire and how many are going keep it from getting knotted up?
What is your insulation type?
How long is the run?
Table 310.15(B)(2)(a) Say's 7-9 CCC's you go to a 70% rating.
Assuming an insulation in the 75 degree column your starting at 205 amps.
205amp X .7 = 143.5 amp
143.5 X 3 =430.5 amp
Really want to do that?
acrwc10 is offline   Reply With Quote
Old 04-18-2012, 06:56 AM   #11
chicken steve's Avatar
sounds like you might consider 3 parrallel pipe runs Cletis......~CS~
chicken steve is online now   Reply With Quote
Old 04-18-2012, 07:14 AM   #12
BBQ
BBQ's Avatar
You would use the 90 column to figure the derating unless the conductors he is using are only 75 which would be odd.
BBQ is online now   Reply With Quote
Old 04-18-2012, 08:22 AM   #13
Cletis's Avatar
Xhhn-2 al
Old 04-18-2012, 12:26 PM   #14
Even two runs would be better, I'm still interested in knowing the length of the run. If it's 4 feet horizontal from one panel to another, go for it. If its a real long run, IMHO, it will "F" up the conductors and be a nearly impossible pull. I just watched a "pool guy" pull a 300' run of #2 thwn through an 1-1/4" pvc and he was using a back how because they could not pull it by hand, "PRICELESS''
Old 04-18-2012, 12:33 PM   #15
Cletis's Avatar
12ft
Old 04-18-2012, 01:03 PM   #16
Phosphate Coated as of 05
dronai's Avatar
Don't you mean 310.15(B)(3)(a) nec 2011 ?
Adjustment factors for more than three conductors in a raceway.
Old 04-18-2012, 10:01 PM   #17
12ft
12' thats just a long nipple, but it will still be a pain in the butt, I'd run atleast two conduits.
I was in the 08' but it was also late when I posted that.
10 k 100 k 200 k ? breaker rating .. what does this mean? realworldelectric General Electrical Discussion 6 12-17-2010 01:59 AM
Standard wire rating vs continuous load rating guitarboyled NEC Code Forum 5 11-30-2010 06:17 AM
Box rating Teaspoon Residential Electrical Forum 6 04-09-2010 02:39 PM
fuse rating CSDC ELEC UK Electrical Forum 3 03-06-2010 02:27 PM
De-Rating simplified? Electrician343 General Electrical Discussion 13 05-02-2009 11:15 AM