Default Define Agricultural Building

AHJ is on me about not having an equipotential plane in a dog kennel.

Is this really an Agricultural building?

If he does give me any lee-way on this, will I establish this grid since footers and slab have been poured.

Only thing I can see in the debate is the fact that the homeowner is calling it a "barn"
shazam is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectrcianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!
Old 04-16-2007, 02:15 PM   #2
Senior Member
 
brian john's Avatar
 
Join Date: Mar 2007
Location: Leesburg VA
Posts: 6,510
Default

There are those here that are better suited to answer this, but that won't stop me. See 547.3 which referes you back to 547.1 (a) and (B).

Does 547.10 apply?

Additionally the NEC discusses livestock hardly equates to dogs. DOES IT?

1. Do these requirements apply?
2. Can you justify this with the inspector?
3. Is there a service what is the grounding electrode for this service, ass the equipotential plane will need to be common with the electrode for the service.
From Wikipedia, the free encyclopedia




Sheep are commonly bred as livestock.


Livestock is the term used to refer (singularly or plurally) to a domesticated animal intentionally reared in an agricultural setting to make produce such as food or fibre, or for its labour.

Livestock reering, (also known as animal husbandry) may be raised for subsistence or for profit. Raising animals (animal husbandry) is an important component of modern agriculture. It has been practiced in many societies, since the transition to farming from hunter-gather lifestyles.
brian john is offline   Reply With Quote
Old 04-16-2007, 02:54 PM   #3
Member
 
shazam's Avatar
 
Join Date: Apr 2007
Location: USA
Posts: 75
Default

Does this apply is what is in question.

I believe the snag is.....Owner has had the building classified as a "barn" on the permit.
There a new service and it is #4 so...
will attaching 4 awg to the rebar in the footer (gotta bust it out first) satisfy his requirement?
I'll be talking to him shortly on the phone.
shazam is offline   Reply With Quote
Old 04-16-2007, 05:23 PM   #4
Moderator
 
Join Date: Jan 2007
Location: Beautiful Cumberland Valley, in PA
Posts: 6,837
Default

NEC wise, the fundamental question is, "are dogs livestock"? If so, the inspector is correct. If not, he is not. I'm inclined to think that a dog kennel or dog breeding operation is fundamentally no different than a cow/pig/sheep livestock operation.
MDShunk is offline   Reply With Quote
Old 04-16-2007, 05:48 PM   #5
Senior Member
 
Join Date: Mar 2007
Location: USA
Posts: 314
Default Property

See Article 547 and this section, animals are considered as property:

"90.1 Purpose

(A) Practical Safeguarding The purpose of this Code is the practical safeguarding of persons and property from hazards arising from the use of electricity."


"547.1 Scope

The provisions of this article shall apply to the following agricultural buildings or that part of a building or adjacent areas of similar or like nature as specified in 547.1(A) and 547.1(B).

(A) Excessive Dust and Dust with Water Agricultural buildings where excessive dust and dust with water may accumulate, including all areas of poultry, livestock, and fish confinement systems, where litter dust or feed dust, including mineral feed particles, may accumulate.

(B) Corrosive Atmosphere Agricultural buildings where a corrosive atmosphere exists. Such buildings include areas where the following conditions exist:

(1) Poultry and animal excrement may cause corrosive vapors.
(2) Corrosive particles may combine with water.
(3) The area is damp and wet by reason of periodic washing for cleaning and sanitizing with water and cleansing agents.
(4) Similar conditions exist.

Article 547 applies not only to buildings but also to adjacent areas of similar or like nature. The requirements in Article 547 address the severe environmental conditions that regularly exist on agricultural premises. Damp and wet conditions, dust from feed and litter, and corrosive agents from livestock excrement are all present in these settings as part of normal operating conditions. Grounding and bonding requirements unique to agricultural settings are necessary due to the sensitivity of livestock to differences in potential between surfaces with which they are in direct contact. The wet or damp concrete common to animal confinement areas enhances this sensitivity."
Joe Tedesco is offline   Reply With Quote
Old 04-17-2007, 06:19 PM   #6
Member
 
shazam's Avatar
 
Join Date: Apr 2007
Location: USA
Posts: 75
Default

Well as it turns out. I will not be REQUIRED to install the bonding for the equipotenial plane....I will HOWEVER be doing it.
I'll sleep better.
shazam is offline   Reply With Quote
Old 04-17-2007, 07:25 PM   #7
Senior Member
 
brian john's Avatar
 
Join Date: Mar 2007
Location: Leesburg VA
Posts: 6,510
Default

And that statement alone; NOT REQUIRED BUT INSTALLING, speaks volumes about the quality of work you do.
brian john is offline   Reply With Quote
Old 04-18-2007, 02:27 AM   #8
Senile Member
 
macmikeman's Avatar
 
Join Date: Jan 2007
Location: Honolulu
Posts: 696
Default

I read up on this a number of years ago and like everything else forgot most of it, but do remember that this affects hoofed animals alot more than animals with paws. Hasn't got so much to do with the feet? (paws/ hoofs) as the hearts of hoofed animals, but since hoofed animals have similar hearts they are affected in a similar way.
macmikeman is offline   Reply With Quote
Old 04-18-2007, 07:35 AM   #9
Member
 
shazam's Avatar
 
Join Date: Apr 2007
Location: USA
Posts: 75
Default

Quote:
Originally Posted by macmikeman View Post
I read up on this a number of years ago and like everything else forgot most of it, but do remember that this affects hoofed animals alot more than animals with paws. Hasn't got so much to do with the feet? (paws/ hoofs) as the hearts of hoofed animals, but since hoofed animals have similar hearts they are affected in a similar way.

Agreed, we were just talking about this a couple months ago at a code refresher. Apparently, cows and such will even stop producing milk.

Thus, my confusion when he said I needed to install an equipotential plane for a DOG kennel.

However, reading the article 547, helped me to understand that it also keeps the metal parts, of which animals may come in contact with, from becoming accidentally energized. So, I feel it best to proceed.
shazam is offline   Reply With Quote
Old 04-19-2007, 01:22 AM   #10
Senile Member
 
macmikeman's Avatar
 
Join Date: Jan 2007
Location: Honolulu
Posts: 696
Default

Quote:
Originally Posted by shazam View Post
However, reading the article 547, helped me to understand that it also keeps the metal parts, of which animals may come in contact with, from becoming accidentally energized. So, I feel it best to proceed.
You almost have it right but lets clear it up for any who read this that do not quite understand the bonding grid. It does not help to keep metal parts that animals might come in contact with from becoming accidentally energized, but rather keeps all metal parts that animals might come in contact with at the same voltage potential, thereby reducing the possibility of a shock to the animal. The metal parts might be accidentally energized by some fault in the system, but if all metal and conductive surfaces(concrete floor) are at the same raised potential, then in theory there will not be a way for current to flow thru the animal. I say in theory, because I would not like to try testing this on myself at home in case there are any holes in the theory.
macmikeman is offline   Reply With Quote
Old 04-19-2007, 05:30 AM   #11
Senior Member
 
JohnJ0906's Avatar
 
Join Date: Jan 2007
Location: Baltimore, MD, USA
Posts: 3,486
Default

Quote:
Originally Posted by macmikeman View Post
Quote:
I say in theory, because I would not like to try testing this on myself at home in case there are any holes in the theory.
C'mon! take one for the team!
__________________
John from Baltimore
"One day at a Time"
All responses based on the '08 NEC
It's not my fault, it's not my problem, I'm not your solution.
JohnJ0906 is offline   Reply With Quote
Old 04-21-2007, 02:04 AM   #12
Senile Member
 
macmikeman's Avatar
 
Join Date: Jan 2007
Location: Honolulu
Posts: 696
Default

Quote:
Originally Posted by JohnJ0906 View Post
C'mon! take one for the team!
Wouldn't work, cause now that I got back into skateboarding at 52 my feet are all caloused on the bottom and would impose too much impedence on the conductor.
macmikeman is offline   Reply With Quote
Old 04-21-2007, 08:11 AM   #13
Senior Member
 
brian john's Avatar
 
Join Date: Mar 2007
Location: Leesburg VA
Posts: 6,510
Default

This is also utilized in substations.

http://www.osha.gov/pls/oshaweb/owad...ARDS&p_id=9871
brian john is offline   Reply With Quote
Old 04-21-2007, 08:44 AM   #14
Member
 
shazam's Avatar
 
Join Date: Apr 2007
Location: USA
Posts: 75
Default

Quote:
Originally Posted by macmikeman View Post
You almost have it right but lets clear it up for any who read this that do not quite understand the bonding grid. It does not help to keep metal parts that animals might come in contact with from becoming accidentally energized, but rather keeps all metal parts that animals might come in contact with at the same voltage potential, thereby reducing the possibility of a shock to the animal. The metal parts might be accidentally energized by some fault in the system, but if all metal and conductive surfaces(concrete floor) are at the same raised potential, then in theory there will not be a way for current to flow thru the animal. I say in theory, because I would not like to try testing this on myself at home in case there are any holes in the theory.

This reminded me of a story the class instructor was telling us during my code refresher.
We were discussing equipotenial planes at the time....

He said that a man got into his shower and turned the water on and when he stepped onto the metal drain cover, that he was electrocuted.

Thoughts?

I think, how on earth? :scratchinghead:
My metal drain is attached to DWC (PVC drain/waste).
Was the metal shower head carrying a potential voltage, if so how did the drain act as a source to ground. If it was a concrete floor slab verses wood members, would this do the trick?
OR did the floor drain have the fault? and the water to the shower head which would have been part of the EGC in the residence provide the path?
I really get blown away by this stuff.
I find it frightening that something like this can happen, it keeps me routinely checking behind my guys.
shazam is offline   Reply With Quote
Old 04-21-2007, 09:54 AM   #15
Senior Member
 
brian john's Avatar
 
Join Date: Mar 2007
Location: Leesburg VA
Posts: 6,510
Default

A few years ago in Maryland a young man was entering a hotel from the back door the door was equipped with an electric lock. The door frame was not grounded and the energized conductor was shorted to the frame, it was raining and he was opening the door standing on wet concrete (from the rain) and was electrocuted. There are cases like this all over the country, very sad and in most cases preventable, in this case I believe they found there was no EGC to the lock and hence the frame was not grounded.

(AP) A pastor performing a baptism was electrocuted inside his church after grabbing a microphone while partially submerged, a church employee said.

http://www.cbsnews.com/stories/2005/...in995829.shtml

Last edited by brian john; 04-21-2007 at 09:58 AM.
brian john is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
135 foot Building sgr1 Workplace Safety 15 12-05-2008 03:44 PM
Ground rods at a remote building heel600 NEC Code Forum 7 05-05-2008 08:58 PM
Building Electrical Services - whose responsibility BIGEYE General Electrical Discussion 1 02-01-2008 07:17 AM
How Would you Define Potential?? mikewardjr General Electrical Discussion 6 08-19-2007 11:51 PM
4 service entrances, one building Magnettica Services and Service Equipment 4 05-11-2007 08:08 PM

Top of Page | View New Posts

All times are GMT -4. The time now is 10:06 AM.


Electrician Talk © 2006 - 2009 The Building Network LLC

Search Engine Optimization by vBSEO 3.2.0