Old 05-01-2012, 06:59 PM   #1
Default derating on roof
need a little help when running conduit on the roodf i know i need to be 2 feet high on the roof, but if u only have 3 wires in conduit do u still have to derate ? my boss is telling me i do whitch i dissagree what does anyone think
ufcc is offline   Reply With Quote
Old 05-01-2012, 07:21 PM   #2
zap
tates1882's Avatar
Well unless you are above 36" then you need to add the value out of table 310.15(b)(3)(c) to your average ambient temp then do the correction. 2011 code
The Following User Says Thank You to tates1882 For This Useful Post:
ufcc (05-01-2012)
Old 05-01-2012, 07:48 PM   #3
The adjustment factor for more than 3 current carrying conductors and the correction factor for ambient temperatures both have to be applied. In this case you only have 3 current carrying conductors so there is no adjustment factor, just a correction factor for ambient temperature.
ufcc (05-01-2012)